Why should we use Star-Delta connection in step down power
transformers?
Answers were Sorted based on User's Feedback
Answer / harishchandra
in Y the vL=1.73*vp
in delta vl=vp and current IL=1.73*ip
also for distribution required 230 n 433v so neutral is
required so we used y - delta conec.
| Is This Answer Correct ? | 23 Yes | 7 No |
Answer / hussain
Actually we use Delta-Star connection for step down to get
neutral in the secondary. The question is wrong , should
read why we use delta-Start connection , not opposite.
| Is This Answer Correct ? | 18 Yes | 7 No |
Answer / guest
1:--- actually we used delta -star connection in power
distribution transformer to provide the returning path of
current,because connected load does not balanced so
returning current goes to transformer star point through
neutral wire which always earthed.
2;---In distribution load is being different type like
single phase three phase etc so we have required neutral for
single
phase load which is only possible in star connection.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / pkv
actually delta star trnasformer used in step down
trnasformer to avoid earthfault give effect of over
current on hv side of the trnaformer
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / arindam
Delta is mainly used on low voltage side because its line voltage=phase voltage. if it is used on high voltage side due to high voltage in phase more insulation is required. But if it is star then its phase voltage = (1/√3)phase voltage. so if high voltage applied to line of star its phase value decrease by √3 times and comparetively less insulation is required. Hence star-delta is used for step down and delta-star is used for step up.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / rafeek
question is wrong,
normally we use delta-star connection for step down
transformer to prevent earth faults.
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / paramesh
Because starting voltage of the star connection is less
compare 2 other connections..........
| Is This Answer Correct ? | 6 Yes | 17 No |
what is relation between ct and pt ratio with multiplication factor of a energy meter? is there any other factor on which multification factor depend?
Which do you think is the most significant cause of energy loss in a factory?
I am an electrical power engineer and arranged power system for a data center, I installed MCB, ELCB and erthing system TN-C-S. But some times several ELCBs Disconnect circuits at the same time! what may be the reason? (the ELCBs are 25A ,30mA)
Iam deepthi.i completed my b.tech from electrical engineering.i want to prepare for civil services.i dont have much knowledge about these exams,but i have great zeal of cracking exams.plz provide me suggestions to which options i can select for optionals
In three phase energymeter the spindle rotating backward why?
how work the differential protection relay in details?
Why Dyn11 Transformer is selected for distribution transformer?
3 Answers JK Associates, MSETCL Maharashtra State Electricity Transmission Co Ltd,
how much current does 3ph. 10 hp ac motor draw.
Please explain how to do 'tan-delta test' on AC generator? and where i get clear and brief detail, give any web page address.
What is Goerges phenomina to start SYCHNOUSMOTOR?
how to calculate the no. of turns in secondary side of CT?
in which direction real power and reactive power flow and why???????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)