I am an electrical power engineer and arranged power system
for a data center, I installed MCB, ELCB and erthing system
TN-C-S.
But some times several ELCBs Disconnect circuits at the
same time! what may be the reason? (the ELCBs are 25A ,30mA)
Answers were Sorted based on User's Feedback
Answer / chandra
Mr. Mehdi, Do check the neutral of all circuits wether they
are connected to same ELCB group. If one neutral from one
group is connected to other group this problem will occur.
Even though all neutral is common at final point, each
neutral will have to pass through the ELCB in order to
monitor the return cuurent.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / prashant
that means tgat u wer using those 30 mA ELCB to feed ur ac/
power sockets or some other heavier load
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.p.sharma
Mr.chandra & mehndi is right and the normally mA of ELCB
used IS AS BELOW:-
1. FOR DOMESTIC = 30MA
2. FOR COMMERCIAL BUILDINGS ETC = 100MA
3. FOR INDUSTRIES = 300MA
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nageshwaran.n
Hi boss, check the connections properly.
Check for:
1. Total Load on MCB's. It should not exceed the market
rating.
2. For ELCB's, check the circuit for the leads interchange.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / mehdi
there wasn't any Falctuation in cicuits. it is strange that
if any problem occured in one circuit others may not be
failed!
I solved my problem by replacing those ELCB with 300 mA
Type!
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pillay
the choice of 30 ma is correct,
or in fact we should be able to
decide what ma rating we want
to choose where.
It could be the fault current was
quite big but fault current could
not be grounded fast enough resulting
in the current floating into other
neighbouring cct resulting in triggering
of the elcb,s.The other solution would
be checking the grounding connections from
the earth pit to upwards and also the actual
earth resistance measurements.
| Is This Answer Correct ? | 0 Yes | 0 No |
Dear Mahdi
Some Current is leakege in earth form circuit and
equepment . so your ELCB was trip.so frist check the all
circuit .
you are using TN-C-S earthing .in this common earth use
for nutral and grounding .
I suggested you for use TN-S type earthing .
| Is This Answer Correct ? | 0 Yes | 1 No |
ELCBs Disconnect circuits at the power fluctuation time or
any other reason????
| Is This Answer Correct ? | 0 Yes | 2 No |
what is the difference between synchronous & asynchronous generators
What are the different types of dams?
sir, iam a electrical engg graduate and i want to go in automation sector and for this i have decided to do industrial training for this,plz suggest me some good institute for the same in delhi,ncr. my degree percentage is 58%, can i get job after doing training, plz help....
What are the maximum and minimum ratings of MCB,MCCB,ACB,OCB,VCB and SF6 breakers?
2 Answers ABB, SK E&C, Sodexo,
expansion of rccb
what is the use of spherical metal balls attached on to the earth wire of transmission over head lines?
transmisssion type
how to make a solar panel? why solar panel cell connected to serious?
why the rating of transformer in k.v.a
does the Trivector Meter of three phase automatically takes care of the low power factor and gives the reading accordigly or it does not take care of the Power factor while giving the readings please explain
What kind of preventive maintenance are there for AC generator?
if three phase supply is given to single phase transformer, what will happen?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)