What are the procedures followed for underground cable
laying.....???
Answers were Sorted based on User's Feedback
Answer / ecstacy006
so many factors to consider for ug cable laying.firstly the
depth to wch cable should be laid ,it may vary with the
company priciples but not less than 1.2m
then over the cable should be filled with pure sand and over
the sand the protective slabs to be placed.the feeder name
should be indicated on the cable with yello paint.
some places where we cant make enough depth we use HDPE(high
density poly ethylene)pipes.through that pipe we lay the
cable.(depth 50-80cm)
when we lay cable on bridges we cant make depth ,here we can
use GI(galvanized iron)pipes.
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / thabiso
nower days cables are suspended by hooks on tha roof to
prevant then from damages and water.note that the hooks are
not permanently installed
Is This Answer Correct ? | 2 Yes | 2 No |
how to calculate diesel consumption of diesel generator by considering load and capacity of generator?
Whag is the PS class of accuracy of CT?
What happens to a line-frequency of high-frequency transformer when it is first energized/ re-energize?
WHY WE GENERATE 3 PHASE POWER ONLY AND NOT 4 OR 5 OR 6 PHASE??? PLS REPLY.
difference between load bus and dead bus?
Cb closed condition if there is a tcs fail whether cb will trip or not
I have a small system with two motors that are running on 380 vac, 60 hz. These motors are expensive and I usally get them from Brazil. I am adding another motor to the system, but I want to purchase a 480 vac, 60 hz motor to use. It will be on a VFD that is rated fro 380 thru 480. Is this posible and will I have to use a larger motor and derate it?
0 Answers US Electrofused Minerals,
from which formula we select a capacitor rating?
WHAT IS A LINE CURRENT AND PHASE CURRENT
What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.
0 Answers Bhushan Power Steel,
What do you mean by PT-100?
two transformer connected in parallel.tap change are different.if i want to on the buscoupler what happen?