Whether capacitor loads can be connected for testing a
diesel engine at its full load capacity? Is there any
limitation of capacotir load? Which is the best load for
testing DG sets?
Answers were Sorted based on User's Feedback
Answer / sudhir
Capacitor is not suitable load for Engine testing, It will
trip high Voltage of AVR if it is sycronous generator.
Best loag for testing resistive.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer 1 is correct.
Normally a resistive load is used for testing a DG. As most
DG's are rated at 0.8 lagging power factor the resistive
load is calculated at unity power factor load on the DG.
This is usually 80% of the kva rating. This tests the
engine to full load.
Where it is required to test the generator at full load
also an induction load is used together with the resistive
load to give the correct power factor.
Capacitor loads are not normally used as DG's do not
operate safely on leading power factors.
| Is This Answer Correct ? | 1 Yes | 0 No |
voltage of a ckt is measured by volt meter having an input impedence camparable with the out put impedance of the ckt Eror caused is 1. Gross Error 2. Errors due to lloading effect
what is tpdt
how can u do the earthing of an aeroplane?
kindly tell me how the load on generator increase by just increasing the fuel of prime mover, as if for exampple 20 MW gen set is synchronized the load ramps from zero to 20 MW gradully and during this procress only fuel of prime mover increases. Which thing determines the load on generator with respect to fuel
HELLO SIR, IAM PREPARING HPCL EXAMS. SO PLS SEND MATERIAL OF HPCL ELECTRICAL ENG..TO VIJAY_8888@YMAIL.COM
What is the formula to calculate the rating of a three phase trnasformer
how can we find thae value of capacitor for single phase motor. what is difference between starting capacitor and running capacitor.
defination of reactor
i want the formula of total eletical knowledgement
A 100KVA SINGLE PHASE TRANSFORMER 10000/200V,50HZ REQUIRES 300V AT HV SIDE TO CIRCULATE FULL LOAD CURRENT WITH LV SHORT CIRCUITED.THE INTAKE IS 1000W.THE % OF REGULATION ON FULL LOAD AT 0.8 PF LAGGING WILL BE HOW MUCH AND THE SECONDARY TERMINAL VOLTAGE ON 0.8 PF LEADING WILL BE
what is the difference between UPS & Inverter
mostly the questions were from machines... d.c. machines, transformer, synchronous and induction all theory paper........ few from power system... but the level of paper was easy.....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)