125Kva Dg can take up how much amphere load.
Answers were Sorted based on User's Feedback
Answer / debaraj das
125 KVA DG = 174A ( In 100% Load)
80% Load of 125 KVA DG = 140 A
( 80% is the Safer load you can give to your DG Set)
Is This Answer Correct ? | 59 Yes | 6 No |
Answer / guest
V= 415
KVA = 125
A = KAV/V*Root3
= 125/415*1.732
= 173.905 Per Phase
Is This Answer Correct ? | 52 Yes | 12 No |
Answer / rajesh
The best answer is 125 Amps.
Normally the best operation is carried at 80% of load.
Is This Answer Correct ? | 20 Yes | 5 No |
Answer / shridhar awasthi
125 kva dg will take 173.90 amps on 100% loading and 191.29
amps at 10% over loading according to I=KVA/sqrt3*voltage
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / nadhan
Why should not we add the capacitor bank for dg set alternator to minimize the dgset load current.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sk aminul hossain
Amp=kva*p.f/volt*root3 So
125*1000*0.85/415*1.732 (k=1000,v=415,p.f=0.85) reactive power
So, amper=147.81A or 148A
Is This Answer Correct ? | 1 Yes | 1 No |
What is the necessary condition for stability.
I have a reading off 1.5ohms at my mem my main c/b is rated at 40/6 amps in a domestic house and i was told to change it to a b curve c/b is this ok
Why do u join toreent power ?
I have 150/1A Rating CT Suppose if i inject 15A in CT " Secondary" means what will happen ??????
1. What kVA rating is required for a transformer that must handle a maximum load current of 8 A with a secondary voltage of 2 kV?
how we calculate electrical load on a building according to area?
Can we use a window type neutral CT instead of a bar type neutral CT. We have an issue with a neutral bar type CT of 800/1 ratio with a Circuit breaker NS800L shneider type, and we want to change it with a window type. Pls advise. Thanks
For a 6.6kV Motor it is recommended to do megger test with 500 V d.c and not more than 5kV d.c but the Hi voltage withstand test should be performed by 12kV AC. Why the dc voltage test should be limited but AC voltage withstand test could be with such a high voltage?
Please explain the following and how these are working with PLC unit 1.I/O Module 2.I/O Device 3.Adaptor Card 4.Ribbon Adaptor 5.RS 485-FC
0 Answers Shree Mayur Engineering,
some meggers have three terminals. wat is the real function of the earth terminal?
a 3 phase motor was running with delta connected, suddenly one phase winding got burnt off, what will be the effect ?
please tell 1 ton equal to how many kilo watt?? in some converter software's that is 3.5 kw. is it right?