what is the size of ht cable of 33kv ht line and
transformers ratings are 2.5mva and 5.5mva.please send
formula also.
Answer / eng. d
first, how will you install it?
underground direct buried, inside trenchs or above ground
any ways, the way to calculate will be done by the cable
vendor but you can do rough estimation
for 2.5 MVA transformer
= 2.5MVA/(1.73*33KV)=43 A
then cable shall be derated and much more than transformer
then we can say we select 60A cable rating
then we go to cable vendor catalog
try to see this
http://www.doncastercables.com/cableCalculator.asp
thank you
| Is This Answer Correct ? | 10 Yes | 1 No |
what is the voltages using in movie theaters??? why ??why not other??
HOW TO CALLICULATE RESITENCE,REACTANCE AND IMPEDENCE VOLTGE OF TRANSFORMER 13.33 KVA 144/240 VOLTS 93/56 A WITH FORMULA
how the specific fuel consumption of 320 kva deisel genarator set (explain with formulas please)?
what is ripple component in ac supply?
transformer is connected with 50hz and 60hz at same rating which will give more output on same rating
what happends when an isolater is operated on on-load
how to calculate cable size for the motor
How can be decreased the size of transformer?
which signal we found accurate reading of analog signal or degital signal and why?
tan delta equation test on alternators
Why different values of B’s (magnetic flux density) are chosen for DC machines and Induction Motors?
Where r use in Dc motor in power plant?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)