what is the size of ht cable of 33kv ht line and
transformers ratings are 2.5mva and 5.5mva.please send
formula also.
Answer Posted / eng. d
first, how will you install it?
underground direct buried, inside trenchs or above ground
any ways, the way to calculate will be done by the cable
vendor but you can do rough estimation
for 2.5 MVA transformer
= 2.5MVA/(1.73*33KV)=43 A
then cable shall be derated and much more than transformer
then we can say we select 60A cable rating
then we go to cable vendor catalog
try to see this
http://www.doncastercables.com/cableCalculator.asp
thank you
Is This Answer Correct ? | 10 Yes | 1 No |
Post New Answer View All Answers
how we test a 3 phase motor on single phase supply....? HOW WE RUN A 3 PHASE MOTOR ON SNIGLE PHASE. supply for testing..? how we verify of a 3 phase motors 6 wire & name thame a1/a2/a3..b1/b2/b3 and c1/c2/c3 for connecting star delta starter ........i have only 1 phase supply ? help forum..........
What is the difference between Encoder and Resolver?
how to select diiferent power transformers of same capacity on no load loss and full load loss by economical point of view.?
What are the advantages and disadvantages of short-pitched winding?
What are the reasons for the parallel operation of transformers?
-What should be minimum value of insulation resistance and maximum value of earth resistance at any electrical instillation and what is method of testing the same.
What is meant by turbo alternators?
HOW TO SELECT THE COPPER CABLE SIZES OF MOTORS,TRANSFORMERS?
If there is major % of Voltage harmonics in the system, how can it be control or reduced?
why we change the direction of winding in rotor ?how we make the north and south pole?
For some transformers we are using solid neutral earthing while some others we are using resistance earthing why ?
where solid grounding and where grounding through ngr done and why?
What is reactance, reluctance,capistance, pls give answeer in hinglish and be simply Jo asani we smajh m aa jaye
How can I calculate per unit (KWH) fuel (Gas/ Diesel both) consumption 1MW unit?
There are different classes of protections in power plants.class a,b,c are clear..is there any class d and e r there..and elaborate class b protection.