Answer / siva
since the losses in the transformer is iron and copper loss
which depend upon the voltage and current but not on the
angle between them
| Is This Answer Correct ? | 25 Yes | 1 No |
Answer / veerendra
the transfor rating is in kva because as the iron losse &
copper losses in transformer depend on the volage & current
so depending on the losses the heat geeration occurs & hence
the rating is explained in KVA to give a detail how much
amount of power it can transfer without getting damaged.
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / sangayya s k
the transfor rating is in kva because as the iron losse &
copper losses in transformer depend on the volage & current
so depending on the losses the heat geeration occurs & hence
the rating is explained in KVA to give a detail how much
amount of power it can transfer without getting damaged.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / okereke okorie daniel
Transformer is rated in kva because the efficiency of a
transformer depends on the copper losses annd the iron
losses which are voltage and current respectively, hence
the rating in kva.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / padmaja
The x'mer rating is in kva because as the iron losses in
x'mer is depends on voltage i.e. as per o.c. test carried
out on x'mer & copper losses is depends on current i.e. as
per s.c. test carried out on transformer.
so depending on the losses reflects voltage & current unit.
hence the rating is explained in KVA to give a detail how
much amount of power it can transfer.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sangayya sk
the transformer dus not concider power factor because trans
former's r rating in Kva P= v*i
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rsundareee
The transfor rating is in kva because as the iron losse
depending on the voltage and copper loss depending on the
current,so total loss depending on the voltage and current
so it,s called kva.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / m.gopinath
All ac machines rating is mentioned in kva on name plates
where as dc machines rating is mentioned in kw. In the case
of dc, there is no question of pf as the loads for dc are
always resistive in nature and the pf is always unity. But
in the load can be resistive, inductive or capacitive in
nature in case of ac machines.
Let us calculate current for different loads (ie for
different pfs) in case of ac machines if their rating is
mentioned in kw:
16 MW (not in MVA as in normal case), 132/33 KV T/F
Case 1: For resistive load
HV Current = 16000/(1.732*132*1)= 70 A (approx.)
Case 2 : For inducive/capacitive load at 0.8 pf
HV Current = 16000/(1.732*132*0.8)= 87.5 A (approx.)
observe the above two cases, for a given rating in MW(16 MW)
the current is quiet different and it will depend on the
nature of the load on T/F. This is not in the case of DC as
the nature of load is always resistive.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / uddin
the transformer dus not concider power factor because trans
former's r rating in Kva P= v*i
| Is This Answer Correct ? | 7 Yes | 8 No |
Answer / varun
i m not sure but i thik due to p.f. beacause p.f different
at all time.
| Is This Answer Correct ? | 0 Yes | 5 No |
Hi If connecting a temp generator 670KVA .415kv with step up Tx .415/11kv. I am given Generator impedances Z1 Z2 Z0 to 100MVA base. Do I need to work out the generator fault current by using these impedances i.e gen rating / impedance. Then use this as my source impedance for the calculations that follow.
What is phase cross over frequency?
what is Real power and Reactive power ? what is difference between them ?
If i have two 3000 kW motors and the whole facility requires a 10 MVA transformer. What would be better installing two 5 MVA transformers(one for 1 motor ) or just a single 10 MVA transformer for both of them. Give reasons for your answer.
1 Amp = kva ? 1 Amp =KW ?
how can decide the current rating of oltc
What is Mvar?how significant is in electrical energy transmission?
why transformer rating in kva
If a capacitor bank is having rating 750kvar for 6.6kv. Then for 3.3kv how much will be the rating of capacitor bank.
What is ramp signal?
What are the different types of trap used for Indian & western Toilets?
what material is the electrical housing wire made of? is there any difference for the telephone lines?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)