Answer / sanjeev nair
The formula for calculating the Capacitive kVAr required to
compensate inductive kVAr is kW*sqrt(tan_angle1-tan_angle2).
In your case, you have to check the present power factor
and then the kW.
Suppose, If you have load of 50kW and the power factor is
0.8 and you have a plan to improve the PF to 0.95 then as
per the above formula the Capactive kVAr required to
compensate the inductive kVAr would be 21.
Besides, one should understand and work on the application.
ie, you can go for a 20 kVAr capacitor bank as per the
above if you have 50kW motor working on a pf of 0.8. If
both load and inductive kVAr is varying, then you have to
go for automatic pf control system with suitable banks to
compensate the inductive kVAr.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / chiknabacha
http://www.newindiaelectricals.com/newindia/exports/capacitor/calculation.htm
Please find the calculation for KVAR from the required table
| Is This Answer Correct ? | 0 Yes | 0 No |
How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?
At present how many HVDC lines are there in india
18 Answers HAL, Infosys, KSEB, Kuntham,
What is the capacitance values of 132,220,400 & 765 kV current transformer
what is inrush current in transformer?
17 Answers Bhel, Essar, GMR,
What is the use of starter in tube light fitting.how it works.
I want to know that a 160kva diesel generator contains capacity of 160kva on each phase like R=160 Y=160 B=160 total RYB=480kva or it is total capacity of all there phases like RYB=160kva ... thanks in advance ...
2 Answers jlpl, JP Saraswat Engineers,
How does a system control centre in a utility plant gets the grid frequency of the electrical network (50 Hz or 60 Hz)by the SCADA system?
Please give me a erda placement paper
how calculate the current faut level
WHAT IS M.P.C.B
During Load testing of battery charger with temporary AC Generator .When reach 70% load Generator immediately shutdown .we could not able to Recognize ,what is exactly problem .Please kindly clarify us
what is the mazor difference between the induction transformer and synchonous motor?what is the similarity between them?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)