What is the use of starter in tube light fitting.how it works.
Answers were Sorted based on User's Feedback
Answer / jvino03
Initially Tube light need more voltage during starting time
to get ionization of electrons. So the purpose of Stater is
to flicker or excite the tube light with high voltage,
Stater is nothing but a 2 metals which is in contact during
starting purpose only... After it comes out from the
circuit....
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / biswa
More clarification needed. the choke coil(iron core
inductor) gives rise to the high voltage e=L.(di/dt) where L
is the inductance of the coil. the voltage induced is in the
range of 800-100 volts a.c. this voltage ionizes the gas and
the tube glows
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / biswa
in my previous answer the voltage is 800-1100 a.c
Is This Answer Correct ? | 0 Yes | 1 No |
what is class of SPD and dittels of all class ?
usually why bettery voltage are 1.5V, even if you open a 9V battery there are six 1.5V batteries in series. is it not possible to increase this voltage other than putting in series
what is the purpose of interpose t/f in control and relay ckts?
Which transformer is suitable for 220/11 kV, 60 MVA, distribution , Y-Y or D-Y or Y-D, give comparison for the same.
IN induction motor pf is increased using capacitors.what will be the effect on motor and system when very large capacitor is accidently installed and pf goes leading.
what is the standard duration after failure EB power
Why HT voltages are expressed in 11KV,22KV,33KV and so on? (ie in times of 11)
Befor synchronissation of Generator what test to be carried out.pl.specify with reason.
How to calculate the voltage drop of 4 Core 50 Sqmm SWA cable for a distance of 350 mtrs and what can be the maximum load connected to it?
A 7 storey building has a floor area of 35,000sq.ft on each storey. On the ground floor 11KV electrical sub-station is to be erected. A load of 3kw for every 400sq.ft (p.f is 0.8) is proposed for each floor. fire pump 7.5hp, water pump 5hp, lift 2 nos, each 10hp and 20shop load of each shop is 5kw. calculate a. load each floor b. total load of building c. L.T feeders for aech floor and from transformer to main. d. distribution diagram e. capacity of sub-station/capacitor bank f. line diagram
new 90kw motor installed so how I purchased cable ,fuse,etc please give me technic for cable selected why always capacitor delta connection
Please give me a solid reason there are 2 ELCB's If we take Phase from ELCB NO:1 an Netural from ELCB N:2 why ELCB is tripping when we connect the Load?please brief me with detail