how calculate the current faut level
Answers were Sorted based on User's Feedback
Answer / gova
Bus fault level was calculated using symmetrical method.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kapil dev sharma
current fault level is calculated by the following formula.
Isc= (FLC/%Z)X 100
Isc= Short circuit current
FLC= Full load current
%Z= % Impedence
Is This Answer Correct ? | 6 Yes | 3 No |