Answer / prakash chandra tah
once the breaker is closed the anti pumping relay prevent flow of current through the closing coil. this will increase the life of the coil and avoid false operation.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / g.baladhandapani
Anti pumping Relay is used in Circuit Breakers to avoid
closing of CB's immediately after Triping of CB's
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / anirban banerjee
Actually anti-pumping relay is designated by K-94.and it
means that the electrical contacts of that are used to close
the dc line to make the closing of circuit breaker not
possible after one closing i.e. prevents sucessive closing
of circuit breaker.the contacts of it may be used to
indicate the closing of breaker
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / mohammed yousuf khan
Anti-pumping relay is usually used for ACB operation. Once the supply is given to the closing coil of ACB, the closing coil operates and gives pulse input to the relay. so the relay activates and maintains the ACB in closed position. Continuous supply to the closing coil damages it.
Generally a contactor or auxiliary relay is used as an anti-pumping relay
Is This Answer Correct ? | 0 Yes | 0 No |
Difference between Earthing Truck & Earthing trolly for HT panel
what is negative current?
Form S and "c" license application both are same? @ tneb portal
can u please mail me the syllabus for GET exam for damodar valley corporation?
Are Refrigerators & Deep Freezers the Inductive load ? How to calculate the Power Factor & hence the Output Power for them ?
If the output of a 100kva, 415v generator is stepped up to 11kv with a 500kva transformer,can the transformer be Loaded above the source generator loading?
give me name of current and volatge control device
WHAT IS THE FAULT WHEN 100HP TURBINE MOTOR TRIPS, LIST THE FAULTS AND ITS TRABULESHOOTING TIPS.. MY AUTO TARNSFORMER STARTER TRIPS
why in scott connection of transformers, main transformer is tapped at 50% and teaser transformer at 86.6%?
5 Answers Bhel, Bosch, College School Exams Tests, Wipro,
What kind of preventive maintenance are there for transformer?
what is ACB
for a machine R=130 KVA Y=132 KVA B=144 KVA Then what will be the total kva