what is the Excaste meaning of CT Saturation??
10 P 20, 15 VA, what is the meaning of 10, & 20.
if the CT polarrity changed what will happened??
what is the differece between measuring CT & Protection CT??
what is the Saturation Point of measuring CT & Protection CT??
Answer / ritesh ashok jaiswal
CT SATURATION MEAN CORE LOSS THE CAPACITY OF HOLDING THE
FLUX .THAT IS THERE IS NO OUTPUT AT CT SECONDARY .
15VA, class 10 P 10 CT means ratio error of prescribed
limit are constant up to 10 times rated primary current
when secondary burden is 15VA.
POLARITY CHANGE DEPENDS UPON FOR WHICH PURPOSE THE SAID CT
IS USED.
Measuring CT :-
 Use for measurement purpose.
 Accurate within the specified working range of
rated current (1% to 120% of rated current)
 Designed to saturate for more than 1.2 times
current to safe the measuring instrument from sever strain
caused by heavy over current.
 Accuracy is not required at high over current.
 High permeability core material with low saturation
level is most suitable ( Nickel- Iron Alloys).
b) Protective CT :-
 Use for protection purpose.
 A protective CT is required to faithfully transform
the primary current throughout it’s entire range from
normal load current to short circuit current.
 It should be accurate at all higher value of
current up to rated accuracy limit of primary current.
 To get high saturation level, grain oriented steel
are used for core.
GENERALLY the Saturation Point of measuring CT 30 VOLT &
Protection CT IS 300 V OR DEPENDS UPON MANUFACTURE TO
MANUFACTURE
| Is This Answer Correct ? | 6 Yes | 1 No |
if the load is reactive then what is the use of calculating the real power and what is the use of reactive power if my question is wrong please excuse me..
Why we make earth connection with Transformer Body and What will be the minimum size of copper wire as per code with respect to KVA rating of Transformer?
what is the function of series reactor
3 Answers Adhunik, INOX, RMSI,
Why grounding is generally done in supply end?
i need to calculate high voltage line power factor daily basics but there is meter reading kwh and kvah while calculating power factor kwh/kvah formula was right. for examble there is point c=13kwh c=1.8 lag c=1.2 lead and c=14.5kvah like that i know that p.f =kwh/kvah but c=1.8lag kvarh and c=1.2lead kvarh points i dont know if u know please reply
will a fluorescent bulb work when dc is passed through it?? if not why??
What is MS-EXCELL?
how can we convert 48V dc into 12 V dc? Any standard device for it??
how can we calculate the cooper armed cable size if the protection load of main fuse is 80 ampere.
in india,we use 230V,50 Hz,whereas many other countries use 110V,60Hz.what r d advs and disadvantages of each of them?
can we start slipring motor on star delta like we start induction motor ? if yes where will we connect ?
what types of fault occurred in transmission line ? which protection function senses the fault?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)