How to calibrate DP tramitter in flow measurement
application? consider my range of flow is 0 to 2000 kg/hr ?
please give calculation of , How much pressure applied on
low pressure side and high pressure side please give detail
of calculation ....
It so important for me please reply as soon as possible
Answer / suresh agravat
0 to 2000 kg/cm2 range
Formula:- URV-LRV=Span/4
2000-0=2000
2000/4=500
0=4mA(0%)
500=8mA(25%)
1000=12mA(50%)
1500=16mA(75%)
2000=20mA(100%)
| Is This Answer Correct ? | 0 Yes | 1 No |
I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.
How many ohms are required for proper earthing?
in rotark mov in display err msg showing how to remove the error
How to Calibrate variable Head flowmeter (Orifice), here we dont know High pressure and low pressure then how to apply pressure on HP and LP side ?
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
tell me about the instrumentation,what is the actual need of it ?what are the characteristics of a IC engineer ?
Wht is Dry Leg Calibration and Wet Leg Calibration?
Hi at present i m wrking with tire industry as a manager having gud ctc. Nw I am selected for 1 of the best chemical industry but my ctc is lower than current n also i hv 2 compromize vit post as post is also lower. I hv 6 yrs of exp in various type of industry. Should i join chemical industry as there ar lot of gud instrument than tire? Financialy i can manage 4 more 2 yrs. Bt during wrking vit tire industry i found there is very less instrument n feel that opportunity is less. Pl ans quickly. I have less time to decide.
what is positive feedback and negative feedback?
1. How many output signals do wew have in process control? 2. Could you write down the names of the pre-commissioning and commissioning stage test instruments and explain them (more than 5 items)? 3. What is the first step to commission a transmitter on service? 4. What is RTD? 5. Find the output value in MA of a temperature transmitter (RTD Type) at 120degree celius? 6. What is the O/P signal of a pneumatic transmitter? 7. What is the O/P signal of an elctronic transmitter? 8. What is the close loop and open loon?
How to convert m3/hr in tonnes/hr
What is exact difference between the panel earthing and system earthing in DCS system. What is the value of resistence.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)