1. How many output signals do wew have in process control?
2. Could you write down the names of the pre-commissioning
and commissioning stage test instruments and explain them
(more than 5 items)?
3. What is the first step to commission a transmitter on
service?
4. What is RTD?
5. Find the output value in MA of a temperature transmitter
(RTD Type) at 120degree celius?
6. What is the O/P signal of a pneumatic transmitter?
7. What is the O/P signal of an elctronic transmitter?
8. What is the close loop and open loon?
Answers were Sorted based on User's Feedback
1. Two output signals are used in process control -
analogue and digital.
2. RTD - Resistance Temperature Detector for temperature
measurement upto 600°C.
3. O/P signal for pneumatic transmitter is pneumatic signal
3 - 15 psi
4. O/P signal for electronic transmitter is electrical
signal 4 - 20 mA, 1 - 5 volt.
5. Close loop having sensor, transmitter, controller, and
controlling element (like control valve, on off valve,
damper, servo motor). Open loop does not have controlling
element. open loop is used for only indication in control
system.
| Is This Answer Correct ? | 21 Yes | 0 No |
Answer / biswarup das
Answer of Ques No.5)) Transmitter(Tx) o/p depends on
calibration range. If the Tx is calibrated in the range
0-120degC. Then it will show 20ma when the actual
temperature would be 120degC.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / kalla anil kumar,jeypore
1- it may analog and digital, or
2- lot of test instruments like pressure calibrator dead weght testor,(DRUCK),temperator calibrator DECODE BOX,temp bath,For control valve mA source,for vabration (vabolator) etc.
3- we have know the tag,location and application of transmitter,
4-RTD- Resistance temperature detector, it is used up -200 to 600 deg C,
5- first we should know transmitter Range, then we calculate mA, if the range is 120 then 0deg 4mA,30deg 8mA,60deg 12mA,90deg 16mA and 120Deg 20mA,
6- .2 to 1 kg/cm2 or 3 to 15psi
7- 0 to 20mA, 4 to 20mA
8- in a close loop PID control,transmitter, and final control element like control valve,on/off valve, and MOV etc, it will work on auto there will be set valve then controlling out put will come from PID-C, in open loop there will be no set point we have control by manual,
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / p.sharathreddy
4. o/p signal of electronic transmitter is 4-20 mA and 1-10 mV
dc
| Is This Answer Correct ? | 1 Yes | 8 No |
what is mass flow meter principal?
A valve in series with an orifice plate (DP transmitter), is aligned for constant pressure in the pipeline, if there is an error dx, How to align it in process.
Related to control system, What is difference between 4-20 mA active & 4-20 mA pasive signal.
Hi buddies! i am facing a problem and if someone could help me it will be an immense pleasure to me. we have compect logix PLC 1769 2L AO module to Heat @ 52 to 56 Deg C .So if anyone can do please help me out with this problem.I'll be highly grateful.
What is SLPC & MLPC? How it works?
Which topics are covered in Process Control?
Can a Differential Pressure Transmitter be used as a normal pressure transmitter??
Why drum level range is given -500 to 0 mmwc pls give me that answer
difference between DCS @ SCADA system? and how can use in field
define feed forward control loop with example and drawing?
Consider a level troll. i am getting a correct value in 4mA and 20mA. the value in the middle(30 to 60%)is disturbed and i am not getting the appropriate value. what is the solution to normalize the level and to get the correct value..
what is the meaing of calibration curve?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)