How to Calibrate variable Head flowmeter (Orifice), here we
dont know High pressure and low pressure then how to apply
pressure on HP and LP side ?
The situation must be an installed, running system, with a receiver that displays a flow rate from the DP pressure signal, because no one just has a DP transmitter across an orifice plate for fun.
Every differential pressure primary flow element is assumed to be zero flow at zero DP. So the DP low side pressure 'zero' will always be zero DP, or when the 3 valve manifold has its process connection valves closed and the equalizing valve open.
The measured DP represents some flow rate on the square rooted curve of the normalized percentage of span.
In order to determine the DP span value, you measure the actual DP and note what the flow rate reads on the receiver (PLC/DCS/recorder/indicator/controller) at that DP.
Then you can calculate what the DP span value is for the max flow rate that receiver is configured for.
The receiver has some configured flow range: 0-500gpm? 0-1,000 bpd? 0-650pm? Find out what it is.
For example, say you measure a DP value of 700mm wc and that 700 mm wc shows a flow rate reading of 264.5 lpm on the receiver.
You have discovered that the receiver is scaled 0-500 lpm for that DP transmitter and the receiver does the square root extraction.
What is the flow rate as percentage of flow span?
264.5 lpm/500 lpm = 52.9% of flow rate span
52.9% normalized is 0.529
Since the flow rate is the square root of the normalized DP span, you need to square the normalized percentage of flow rate to find the equivalent percentage of DP span.
0.529^2 = 0.2798, or 27.98% (~ 28%) of the DP span.
If 700mm is 28% of span, 100% of span is 2500mm wc.
So the DP span for the transmitter is 0 (no flow) to 2500mm wc (max flow).
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 1 No |
Can we used Condensate Pot on flow transmitter which is using on liquid having sluge and DP transmitter is in pit and below the process line,Can we used Condensate pot for accamulate the Sluge?
What is the basic difference between 2 Wire, 3 Wire and 4 Wire RTD
how can be connected thermocouple in series?what is the need?
how to measure flow with dp
when the operation engineer told you that he gives the control valve order to open but there is no response ! what will you do ? and if you found that there is astuck , what will you do ? (note : it is apanumatic valve )
Specify eight technical requirements that you would consider important, when deciding upon a particular control valve?
You are looking at the RS-485-side of an RS-232/RS-485 converter and the power supply voltage for the converter is +5V. Under idle conditions (no transmission), and assuming you have enabled the RS-485 output: what would you expect at: (a) Output A measured against output B (b) Output A measured against ground (c) Output B measured against ground
What do you know about gail?
In instrumentation standard we use 4 to 20ma for transmission , why cant we use 3 to 19ma ?
Why Ma signal is using for control system?
what is start up vent valve ? why it is used in boiler?
8 Answers ACC, Bhushan Power Steel,
what is working principle of vibration prob