can we change the range of 3151 model level transmitter of
rosemount make? present calibration range is 1000mmwc and
want to change it to 2000mmwc
Answers were Sorted based on User's Feedback
Answer / narayan
Check Tx data sheet or engraved plate on the tx and it gives span limit as 2000mm, then we can change
if it is below 2000 mm, we can not change, or calibrate
it is sensor range
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mudassir
yaa you can but you have check the model no. if it is30512G
THEN YOU CAN CALIBRATE IT upto6000mmwc
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / saumil
We connect 375hart protocol and given this new range and calibrate 20 mA at 2000mmwc
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ramana
If the Tx. Range is 2000 mmWC we can change it. But we need
little calculation. There is one formula
square root of(P1/P2)= Q1/Q2
Where P1= Pressure 1
P2= Pressure 2
Q1= Flow at Pressure 1
Q2= Flow at Pressure 2
Is This Answer Correct ? | 0 Yes | 6 No |
An atmospheric storage tank has a diameter of 20 m and a height of 8m.It is half-full of liquid with the remainder of the space containing air normally at atmospheric pressure. If the connection to atmosphere is accidentally closed off and 10 cubic m of liquid removed, what happens to the internal pressure of the tank? What are the possible consequences for the tank?
can any one tell me when ongc placement test and its forms is available????/ pls tell me if u know
line up procedure for dp type flow transmitter?
Why ues 250 ohms Resistor during hart type instruments calibration with hart protocol in details ?
what is the tempareture conpensation?what is the use of this?
How a oxygen sensor & analyzer work at boiler or furnace, whats the principle & science is beyond this,How O2 sensor sence & convert signal & move toward analyzer & analyzer show reading in percent?
what is the difference between signal cable and ontrol cable?
What are the two states of a controller
Can anyone explain about ELectropneumatics principle?
1 Answers Forbes Marshall, Step,
how can we caliberate interface level troll
2 Answers Grasim, IOCL, KOC, Sankyu,
Why we are measuring 4-20ma? Why we are not taking 0-20ma? Plz answer this
What is the differerence between hysterisis and linearity.