for a 132/33kv transformer secondary is star and is
connected to NER. and from secondary a cable is running to
33kv swbd. since the cable is single core do i have to run
neutral cable also to 33kv swbd.???
Answers were Sorted based on User's Feedback
Answer / parth belani
Since the neutral of the star connected secondary is
already grounded through NER, there is no need to run a
neutral cable.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ramesh
there is no need of taking neutral point unless u need.Because mostly in 33kv Switch board you will feed 33/11Kv or 33/6.6Kv Transformers ,which will be mostly in (Dyn11 ior Dyn1) or to any other 33KV boards. Any how you are not going to take any motors load directly in 33kv.so it s not neccessary. but if you feed any star connection load in Primary you need to take neutral point.
| Is This Answer Correct ? | 0 Yes | 0 No |
It is not necessary to run a neutral cable as the same is
not requried for a 33 kV 3 wire AC system. But you need to
be cautious about the circulating/eddy current (since in
is a single core cable) which flows through the screen of
the 33kV cable. The voltage genrated by the circulating
current should be more than 130 V as per IEC standards. In
case of heavy circulating current the cable would get
heated up. You may do earthing of the cable only at one end
and leave it open at the other end. In case of a very long
cable with joints in between, mid point bonding is
suggested.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / indreswararo kota
for a 132/33kv transformer secondary is star and is
connected to NER. and from secondary a cable is running to
33kv swbd. since the cable is single core do i have to run
neutral cable also to 33kv swbd.???
| Is This Answer Correct ? | 0 Yes | 2 No |
what is feeder?
How to calculate Earth busbar size & what is the procedure we make for determine that?
Why we called L-G fault as line to ground fault why ground? suppose if a line falls on building roof then can we called these fault as line to roof fault? please explain why ground term is used here?
how to calculate the earth fault current
define transient state &steady state
why choke is provided in the centre of the tube light?
in power station power measuring unit is KW but in transformer is KVA why?
What are the various reasons for an inductin motor to get heated?
all details of DG UPS HVAC
pls someone send me sample question papers along with the key.thanks in advance
What is the diffrence between ofline ups and online ups?
What is the most accurate way of testing ELCB?ELCB is better than RCD?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)