Answer / dipak patil
the tf cu losses are proportion to current and irone or no-
load losses are propotional to voltage rating of
transformer. Since losses once available it is essy to
calculate transformer efficiency. Hence tf rating is given
in KVA insted of KW
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / engr. sumair mir
p.f=kw/kva .... T/f rating is in kva bcoz ,
1- Power factor of the load is not known.....
2- T/F losses depends upon cu- losses(due to current) and
core losses(due to voltage).
due to these resons t/f ratings are in kva.
while for motors and other machines the rating will be in kw
becoz their p.f is known(ranging from .2 to .8 during light
load and peak load period)...
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / srikanta
generally ratings of electrical machines are depends open losses and power factor.
in case of transformer copper loss depend on current and iron loss on voltage but independent of load power factor,hence it's rating is KVA rather than KW.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mahmood al-ali
1- Any transformer includes core losses and copper losses
2- Core losses are based on input voltage
3- Copper losses are based on current flowing through winding
4- Therefor, total losses are based on voltage in addition to current but not power factor.
Thus, the rating of transformer is done in KVA not in KW
| Is This Answer Correct ? | 1 Yes | 0 No |
Hi, what is 100 % stator earth fault protection and how it can be achieve by 3rd harmonics and low frequency injection principle ?
Regarding units, for voltage we are denoting Volts as V but in case of current we are not denoting Ampere as A instead as I..Why..? Any technical reason for this..?
in 33/11kv stepdown transfomer, transformer will stepdown to 11kv & remaining 22kv where it will go..
will a transformer work when pulsating dc id applied to its primary?? what will be the result??
why is the earthing pin on 3 pin top are big and thick
how to cal calculate capacitance in DC Circuit
what is current
hi all i like to know vat is power plot in control systems also i want to know abt latest trends in electrical & electronics
what is the ms flat constant for calculating earth mat design calculation?
For 35 HP motor how much amount of capacitor should be on in kvr to reduce the current bill
what is the pperating squvance in transmission line for circuit braker, isolater & earthing switch.
what r the main parts of central chiller plant in Air conditioner ? explain the function of each?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)