why we are using auto transformer in sub station mostly???
Answers were Sorted based on User's Feedback
Answer / tuhin
an autotransformer will be smaller than an equivalent
conventional transformer. The reason is an autotransformer
essentially has one winding on a core, with one tap
including the whole winding, and another tap including only
part of the winding. In a conventional transformer, power
is transferred from one winding to the other by induction.
In an auto, some is by conduction, and some is by induction.
Here's an example comparison:
Say we have a 10MVA 100kV/50kV 3 winding auto transformer.
There are two parts of the winding - the series winding
(the section of winding between the 100kV connection and
50kV connection), and the common winding (the section of
winding between the 50kV connection to the neutral). If
powered at 10MVA (full load), there will be:
10M / (100k * sqrt(3)) = 57.7 Amps flowing into the
primary, and
10M / (50k * sqrt(3)) = 115.5 amps flowing out of the
secondary
So, 57.7A flow into the primary, down through the series
winding and out the secondary. At the same time 57.7A flow
up from the neutral through the common winding and out the
secondary, resulting in a total secondary current of (57.7
+ 57.7) = 115.5 (sorry, rounding is making my math look
wrong!).
Thus, the series winding is handling a total of:
(100k - 50k)* 57.7A*sqrt(3) = 5MVA, and the common winding
is handling a total of:
(50k - 0) *57.7A*sqrt(3) = 5MVA
So the series and common windings only have to be made to
handle 1/2 the total load(for this example - it is 1/2
because the primary / secondary voltage is 2/1). In a
conventional transformer, each winding carries the full
load (10MVA), because it operates on induction (no
conduction).
If the votlage ratio between primary and secondary is too
high, there is no real net savings in size (and thus cost),
so a conventional transformer is often used. The cutoff
point is around 4.
Is This Answer Correct ? | 8 Yes | 4 No |
Answer / sivachandran
Auto transformer is a single winding transformer. In auto
transformer single winding is works both primary and secondary
Is This Answer Correct ? | 4 Yes | 6 No |
What happen Grid EARTH plat got cut.
why DG sets power factor is 0.8 lagging.
i have a Connected Load of 280KW and Maximum Demand of 224KW to one of SMDB under design with me. which criteria should i consider to design panel and main cables connected Load or Maximum Demand 1)Breaker rating 2)Panel Busbar rating 2)Incommer cable sizing (ignore Voltage drop)
IF I USED VVVF DRIVE IN FAN APPLICATION MOTOR IN 6.6 KV ( 700 KW) MOTOR & DURING NORMAL RUN OPERATION TIME IF RPM SUDDENLY REDUCE IN MOTOR BY DRIVE(E. MOTOR RPM REDUCE SUDENLY 687 TO 550 RPM) WAHT WILL BE HAPPEND IN DRIVE
what is EBXl (electron beam cross linked ) cable ?
How to distinguish between the armature wires with the field wires of a Dc motor ?
state working of halogen lamp?
purpose of breaker contact multiplication relay?
What is neutral earth voltage of transformer and what should be the value
In Transmission System if the potential difference at the two end of line are same then is the transmission of power will continue ? if yes then how.
what do you know about SERVOMOTOR
will the introduction of capacitor bank parallel with the induction load reduce power consumption
4 Answers Nokia, WAPDA Water and Power Development Authority,