why we are using auto transformer in sub station mostly???
Answers were Sorted based on User's Feedback
Answer / tuhin
an autotransformer will be smaller than an equivalent
conventional transformer. The reason is an autotransformer
essentially has one winding on a core, with one tap
including the whole winding, and another tap including only
part of the winding. In a conventional transformer, power
is transferred from one winding to the other by induction.
In an auto, some is by conduction, and some is by induction.
Here's an example comparison:
Say we have a 10MVA 100kV/50kV 3 winding auto transformer.
There are two parts of the winding - the series winding
(the section of winding between the 100kV connection and
50kV connection), and the common winding (the section of
winding between the 50kV connection to the neutral). If
powered at 10MVA (full load), there will be:
10M / (100k * sqrt(3)) = 57.7 Amps flowing into the
primary, and
10M / (50k * sqrt(3)) = 115.5 amps flowing out of the
secondary
So, 57.7A flow into the primary, down through the series
winding and out the secondary. At the same time 57.7A flow
up from the neutral through the common winding and out the
secondary, resulting in a total secondary current of (57.7
+ 57.7) = 115.5 (sorry, rounding is making my math look
wrong!).
Thus, the series winding is handling a total of:
(100k - 50k)* 57.7A*sqrt(3) = 5MVA, and the common winding
is handling a total of:
(50k - 0) *57.7A*sqrt(3) = 5MVA
So the series and common windings only have to be made to
handle 1/2 the total load(for this example - it is 1/2
because the primary / secondary voltage is 2/1). In a
conventional transformer, each winding carries the full
load (10MVA), because it operates on induction (no
conduction).
If the votlage ratio between primary and secondary is too
high, there is no real net savings in size (and thus cost),
so a conventional transformer is often used. The cutoff
point is around 4.
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / sivachandran
Auto transformer is a single winding transformer. In auto
transformer single winding is works both primary and secondary
| Is This Answer Correct ? | 4 Yes | 6 No |
if we have a industrial load of 400 kilowatts with 415 volt AC then how much total harmonic distortion (thd%) should be acceptable for steady power system.
why does a dc machine has high efficiency while working as a generator than as a motor
define displacement & magnitude ?
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage.
In case of 3 phase motor why it is called single phasing by failure of one phare unless there is rest two phase are acting. ?
WHAT IS DIFFERENCEN BETWEEN CURRENT AND VOLTAGE?
how do you test the capacitor bank ?
Details about Flux Compensated magnetic Amplifer starter for motors
how to determine Sq.mm size of finolex power cables.
what is the difference between MCB & MCCB
Define relative stability.
From stability point of view,What(higher/lower) should be the value of inertia constant of rotating machines?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)