Answer / muralidaran - itc
It depends on Application. In HT conductor sizes will be
less & also motor will be more compact since current flow
will be less, but insulation level be more.
HT will be my choice, if speed controll is not required.
LT will be my choice, if speed controll is required (VFD)
Since HT VFDs are quiet high in cost.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / vinoth
For 300 KW motor we can use LT switchgear. Current consumption of a 300KW motor will mot be more than 1000A. So LT switch gear is possible to use
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / sadam hussain gaad
Depends upon application.
if all other motors are operated on HT/LT then 300 KW motor
should be opertaed on HT/LT respectively.
If your generation is HT and you want operate on LT then
you have to install VCB, Transformer, ACB and size of cable
will be more as compared to HT but less insulation will be
required.
If you want to operate 300 KW on HT then no need of
transformer,ACB, only XLPE cable will be used.
Is This Answer Correct ? | 1 Yes | 0 No |
Is a current transformer step up or step down ?
What is the 415V AC Soft starter? Explain with an example?
if 2500 KVA TRANSFORMER CAPACITY.33KV INCOMING HOW ARE AMPEAR PRIMERY SAID
In my project i am layout cables under the Maintainance bay /Maintainance yard in the TG Building. Whether in this route i can lay the H.T.Cables??? i am taking all H.T cables from the H.T Transformer to the TG Building..
Can any body tell gulf interview question for experienced electrical engineer ?
In a simple spur gear train, gears with 24, 48, 32, 72 and 96 teeth are in sequence. The gear with 24 teeth runs at 900 rpm. The speed in rpm of gear with 72 teeth is
why we used star delta starter for above 5hp motors
why in a swquence network representation, the negetive sequence generated voltage is taken as zero?
ANY ONE TELL ME ABOUT generator synchronization panel panel to synchronise 3 gen of 250kva both automatic and manual. 2 gen output vol 415 3ph, 1 gen output vol 400 3ph SEND THE DETAILS DIAGRAM ON THIS EMAIL ADDRESS ayazleo@hotmail.com as soon as possilble best ragrds electrical engineer ayaz mahmood SAUDI TECH
How does the phase sequence controller works, how it identifies the phases? confirm working principle
1) Can anyone give me a typical value for Insulation Resistance of 11kV xlpe cable? 2) How much will the IR value decrease per KM of cable length added?
How to design the NGR Resistance