Answer / carl_ellis
There is no national or international standard for 24Vdc in
industrial instrumentation and control.
The use of 24Vdc has evolved out of common practice and has
seen global use and acceptance as a 'de facto' convention,
as opposed to a formal standard. The acceptance goes
beyond loop powered transmitters, it goes into discrete
control as well.
The reasons are many.
1) 24Vdc is a low enough voltage to be considered 'safe'.
It is accepted as a voltage level that does not shock human
beings through contact with dry skin.
2) 24VDc is a high enough voltage to do real work with
currents that are practical.
3) An enormous array and variety of field instruments and
controls can be designed and operated intrinsically safe at
24Vdc, not just loop powered transmitters.
4) Loop powered field instruments powered by 24Vdc can
drive 500-600 ohms of load resistance, enough for one valve
positioner (split ranging 2 valve positioners with a single
current output driven by 24Vdc is difficult).
5) Lead acid batteries are useable for battery back-up or
UPS supplies.
6) On the discrete side, 24Vdc is sufficient voltage to
break through oxide coating on switch and relay contacts
7) For discrete control, 24Vdc offers a tolerance band
around binary 'high's and binary 'low's of more than a
couple volts, which allows for operation in a moderate
level of electrical noise.
8) Statistically, 24Vdc devices have failure rates about
half of that of 120/240Vac actuation devices (relays and
solenoids). This a serious consideration for emergency
shutdown or SIS systems.
Carl Ellis
Measure First
| Is This Answer Correct ? | 10 Yes | 0 No |
always field(Process) instruments are communicated or
connected with PLC, DCS system.those PLC, DCS operating
current is 24 Vdc, so that instrument which are connected with
DCS, PLC system will be also using 24Vdc only.
| Is This Answer Correct ? | 5 Yes | 6 No |
What is the use instrument barriers? Can you give me review materials about this?
how to measured k type thermocouple temp.
What safety precautions you will adopt to work on Steam service control valve?
What is a PID?
I am teja. I am studying Msc(tech) Electronics and Instrumentation (3years course) in Andhra university. But my course is not recognised by UGC and AICTE. Please tell me the job opportunities after this course. And i fineshed PLC course in IGIAT ,Vizag.Also complted my short term coure in SCADA, Seimans WinCC in ATI,Hyd.After Msc can i join Mtech for good job? or phd. How i can get good job in INdustrial Automation Side. Please give replay.Because this is my life matter.
On liquid service if PT Head is 18 meters. How much pressure will be exerted on it. If Transmitter is not in service?
what is the usage of QDV & VOLUME BOOSTER.
Somebody ask me how many size of control valve what is mean of control valve size?
PLEASE PROVIDE SAMPLES OF CHEVRON SKILL TESTS
Explain about 4 wire instrument concept & tell about its wiring fron sensor in Field to PLC panel.Explain with an example?
Explain why plc require in analog input 4-20amp & 0-10 volt?
What is exact difference between the panel earthing and system earthing in DCS system. What is the value of resistence.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)