Explain Split Range Control In Control Valve Briefly.

Answers were Sorted based on User's Feedback



Explain Split Range Control In Control Valve Briefly...

Answer / sam

Split range is as per answer 2 and not answer 1. Answer 1 is
using two valves, one is a fail open and one is a fail
close. The 4 to 20mA control signal is then controlling the
two valves but in opposite directions. This can also be done
by calibrating the one positioner as a direct acting and the
other as a reverse acting.
Yes this is 100% correct and can be done and the two valves
will work perfectly and in exactly opposite directions to
each other. In a case like this the two valves will have to
be identical as well otherwise the balancing act you are
trying to perform with this setup might not work.
Never seen a application where you would need this but if it
needs to work like that, it can be done.

Split range means you are splitting a 4 to 20mA control
signal in two.

This is very useful in applications where the product flow
increases very rapidly and then falls away again. a Good
example will be before a slug catcher where the incoming
product from the well heads is coming in suddenly very fast
and then falls away again after a couple of minutes.
Another application is to control the steam from a boiler.
At times you need a lot of steam and other times you only
need a small amount.
How do you size the valve needed to control these very big
changes. a Small valve is needed to control the normal flow
but if the flow increases the small valve will open fully
and it will still be to small to control the now very high
flow or pressure. If you install a big valve to control the
big pressure or flow the valve will only open 2 to 5% most
of the time and it will be impossible to do stable control
with such a valve opening. Say nothing about the plug and
seat that will only last a couple of days.
To control these very high variance in flow and pressures of
the process we install two valves in parallel in the same
line. Normally the one is a small valve and the other is
about twice the size of the small valve.
The design and process engineers will decide what minimum,
normal and maximum conditions are and do the valve sizing
accordingly.
We calibrate the small valve to open from fully close to
fully open with a signal of 4 to 12 mA. We then calibrate
the second bigger valve to open from fully close to full
open with a signal of 12 to 20 mA.

In a situation where you use identical valves you can take
the signal from one controller and send it to both valves
but in the above application it is better to use two
controller but with the same input from one pressure or flow
transmitter. Each valve will then be controlled individually
from its own controller and on it's own PID tuning set. I am
sure you can see that it will be quite impossible to find a
PID tuning set that are appropriate for both the big and the
small valve and it is therefore better to use two
controllers but with the same input.

During normal operations the small valve will control the
process without any problems based on the input from the
pressure or flow transmitter, and the bigger valve stays
close all the time. If the process changes to something
bigger than what the small valve can handle the second
bigger valve needs to help, and will start opening up, once
the small valve is fully open. Once the demand falls away
the big valve will start to close and then the smaller valve
until the process is back to normal operating conditions..
Both valves receive a full 4 to 20mA signal from it's own
controller, but will only react based on the 4 to 12 or 12
to 20mA calibration that was done on each valve's positioner.

In other simpler applications you can use two identical
vales and set their positioners as above and send the one
controller output signal to both. One PID tuning set will
also work for both valves and conditions.

The valve sizes will depend on what the conditions are so
they can be the same or they might need to be different sizes.
Good luck

Is This Answer Correct ?    28 Yes 2 No

Explain Split Range Control In Control Valve Briefly...

Answer / nilesh karpe

In addition wt ANS.1-
in split range control the control signal is split in two
ranges according to the application .for eg,4-20MA.signal
can be used as 4-12 MA. FOR VALVE A OPEN i.e.50%.& 12-20MA
for vlv b open.vice-versa.

Is This Answer Correct ?    22 Yes 2 No

Explain Split Range Control In Control Valve Briefly...

Answer / arunnatraj

split range control is which the output of a controller is
split to two or more control valves. For eg,
For 0% controller output,valve A fully open & B fully
closed.
For 25%, Valve A 75% open,B 25% open
For 50%, Valve A& B- 50% open,
For 75%, Valve A 25%open, B-75%open..
For 100%, Valve A fully closed & valve B Fully Open..

Like this, d controller output action can be set depending
upon the application...

Is This Answer Correct ?    22 Yes 17 No

Explain Split Range Control In Control Valve Briefly...

Answer / www.islamqa.com

perfect answer sam as usual

and if there is something else to say I can say that split
range control ( or call valve sequencing ) is a technique
used for satisfy the procsee requirements.

Actually we have techniques and modes for this strategy.

The used techniques to achieve valve split
ranging /sequencing are:

1 - Valve bench set adjustment (modify the valve itself)
2 - Positioner adjustment
3 - I/P adjustment
4 - Using 1 controller with 1 I/P and 2 adjusted valves
and this is very slow process as we have to wait a long
time till the pressure is built up witin the loop.
5 - using 1 controller with 2 series I/P
and here we face the risk of voltage drop.
6 - using 1 controller with dual o/p.
7 - using 2 controller with the same input.

# And we have 3 main modes for this strategy:

1 - COMPLEMENTARY:
where 1 of 2 valves opening is opposite to the other
@ 4 ma valve-A is fully open while valve-B is fully closed
and thier stems move synchronously.
2 - EXCLUSSIVE
3 - PROGRESSIVE

Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310

Is This Answer Correct ?    6 Yes 2 No

Explain Split Range Control In Control Valve Briefly...

Answer / ferdinand

Split range control in process operations point of view, generally used in pressure control, flow and level control also in controlling temperature.

for example a split range control application for pressure control. the input coming from pressure transmitter is processed by the pressure controller then relays the output split between the two control valves to modulate the pressure of a certain vessel.

There are many variations of split controller, like for expmaple valve A at 49% start to modulates the opening to 0% full open while the other valve starts to modulate at 51% opening to 100% full open. for this example both valve are close at 50%. at 50% it means the set point and the process value are the same so the valves are both close. on this particular example, one valve normally supplies the pressure while the other releases it normally goes to the flare system or other systems that serves the purpose.

The accuracy of the control is due to incorporations of PID. the proportional, Integral and the derivatives that in laymans terms it considers the present, the future and the past in predicting the relays in order to control.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

which instrument is used to study the structure of phloem and xylem tissue?

1 Answers  


what is the difference between plant earth and instrument earth? and what type of cable( cable size ) used for both? and why ?

0 Answers  


What is cascade control in process instrumentation?

4 Answers   Engineers India, ITC Infotech,


Difference between ultra sonic flow meter

0 Answers  


Can anybody explain about wellhead control system.

1 Answers  






How to convert 4 wire level transmitter connection to 2 wire.

2 Answers  


Sir i am preparing for PSU exam for ONGC but i am not able to get the appropriate syllabus and previous year question papers. Kindly send me the same, that will be a great help from ur side. OR if anyone can plz send me the papers and syllabus please.

11 Answers   Bhel, GAIL, IOCL, ISRO, NTPC, ONGC,


testing of thermo-couple?

3 Answers  


the pump holds on run indication into the dcs and filed local control panel remote push button condition operaton wrong like when the push button pushing conditions the pump is off and the push button release condition the pump is on totally opposite condition . And control room inside give the stop command into dcs just 1secon relay engage and again normal condition. How can I slove

0 Answers  


what is the working principle of vortex flowmeter

9 Answers   Essar,


How can I make calculation for Install level transmitter (DP) for open tank and cloes tank?

1 Answers   Petrofac,


Why we are using temperature and pressure as a reference when measuring flow of steam?

4 Answers   Shell,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)