Range 8 Kg/cm2, alarm to be set at 2Kg/cm2, at wat pressure
reciever switch to be calibrated? justify the ans?
Answers were Sorted based on User's Feedback
Answer / shan
we are to calibrate at the pressure switch. Pressure switch
is the pressure reciever.we have to set the pressure switch
at 2Kg/cm2. If pressure reaches 2Kg/cm2,it will alarm.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / mithilesh kumar
1st pr. switch is combination of NO,NC,COMMON.OK.
for setting alarm at 2kg/cm2.
it calibrate with DEAD WEIGHT TESTER at 2kg/cm2.during
calibration NC becomes NO and NO become NC.it check with
multimeter in continuity mode.ok.
if it's done then your calibration is ok.
then you can use as per requirement.
any comment.
most welcome
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / welcome4ujd
if range is 0 to 8 kg/cm2, an d alarm needed is 2 kg/cm2.
that is 25 percent of range, set the alarm at 6 psi of a 3
to 15 psi out put.
and if it is a flow transmitter of some range,say 0 to
1000 mmwc and alarm at 250 mm
then 25 % of flow in transmitter will give square root 25
devided by 10 tht is 50 percent in the control room , so
you have to set 50percent in the receiver switch that is 9
psi for a 3 to 15 psi out put.for basic flow transmitter
to find out square rooting from field to ccr
just square root the input percentage and devide by 10
to find the field input from control room signal
devide the ccr signal percentage by 10 and square it.
Is This Answer Correct ? | 2 Yes | 7 No |
Wht should be the ratio of natural frequency (Fn) to wake frequency (Fw) and wht if goes above the rato limit?
what is the difference between single and double compression cable gland
how u calibate pr tx without master tx?
What materials are used in thermo wells?
How to convert gpm into inches of eater.I nerd formula with example so pls help me.
What is the formula To convert Degree centigrade to foranhight.
What are the cable come out from the paddle type flow sensor.and how is further connections
what is novram ic number of foxboro 762cna microcontroller ?thank
What is the difference between a Extension cable and a copnesating cable.Where can we use compensating cable. Is anywhere compensating cable are used for mv transmission to the indicator.
Q-Explain the different load conditions that will produced different offset which may or may not be acceptable to thhe control function
Why Ma signal is using for control system?
What is a snubber circuit?