i have dry type transformers can you help me that how many
tests i can do to know the performence of transformer and
also please tell me about the BDV test and Insulation
resistance test in oil cooled transformers
Answers were Sorted based on User's Feedback
Answer / s ghosh thakur
The following tests to be done during commissioning.
1.Duster value.
2.PI test The value should be above2.o
3.Tan delta test.
4.Ratio test.
5.short ckt.impedance test.
6.vector test.
7.IR test.
8.Polarity test. Thats are sufficient.
BDV value of TRANS OIL should not be less than 50 kv.
IR value of oil cooled trans should be 100M w.r.t gr.and HT
to LT also 100M.PI test should carried out value min 1.5 to
2.0
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / brijesh soni
yes this ans is right you may be test Oppen circuit test,
Megnetic bellence test And very important Inples test.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nithiya
tan dalta test only for above 220KV higher rating
transformers only conducted , Impuls test only conduted in
factory only..and Asper IS 1866-2000 less then 72KV=40KV,
170KV=50KV above 170KV=60KV.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pinaki chatterjee
according to all routine test as per IS-2026 PART 1 and magnetic balance, also current balance test should be require if necessary temperature rise test can be made.
if the voltage level is 11 kv so IMPULSE TEST AS PER clause 12 can be made for better acivement.
partial discharge should always check
Is This Answer Correct ? | 0 Yes | 0 No |
What is the use of Isolation Transformer, and Neutral is using for return path, finally this current is going.... but same time the voltage of the neutral should be below 1 V...
HOW DO YOU CAN CHECK A 15KV DIODE, WHETHER IT IS OK OR NOT?
What is an alternator impedance value?
what is current
53 Answers Bio Enterprises, CLG, TCS,
why dc supply is given to the field of alternator
how and where does star and delta connection is used ?
How to Convert Gen KW to H.T amps ?
How to find out kvar from any particular load capacity give a formula
11 kv input, 66 kv input advantages
why transformer rating in kva?
what is mind in cable
why swinburnes test cannot be performed on series machines?explain