how much current we can get from 11kv overhead line ?
Answers were Sorted based on User's Feedback
It is depends on the generating station MW capacity
Is This Answer Correct ? | 19 Yes | 12 No |
Answer / prabhukumar
thats depends on the amount of load connected. depending on
that right material and protection will be used.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / a k kataria
Current to be drawn from 11kv line depends on different
factors.These factors are length of line, size of
conductor,ambient temperature of region etc.Normally 11 kv
line with Racoon conductor could carry 197 Amps and perhaps
with Dog conductor could carry 240 Amps with VD 6%.Also
Currents beyond this may create problems at breaker levls
as excessive heat coud result particularly at Joints.
Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mohamed
it is depend on the type of the conductor CU or Al
it is depend on the cross section area of the Conductor
R = resistevity * length / Area
1 MM^2 ----> Cu give between 3 --> 5 Amp.
1 MM^2 -----> Al give between 1 ---> 3 Amp
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / amit
it depends upon how much load is connected and generation side production capacity
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dilip
it is depends on the rating of distribution transformer,e.g
if there is 100 kva, then it will take 5.25amp.
Is This Answer Correct ? | 12 Yes | 14 No |
Answer / mahdi
this depend on headway , capacity of line , heavay of wagon
and dever of rail , capacity of traction motor ...
electrical_powerstation@yahoo.com
expert of OCS in mashhad iran
www.murco.ir
Is This Answer Correct ? | 1 Yes | 8 No |
how calculate kva in to kw
As we use capacitior bank in 3ph ckt for improvement of PF, why not we use capacitor in single phase domestric use, at our house their are many inductive equipments,like fan,mixer,tube choke,air conditioner they also draw PF... by using capacitor can they improve PF. if yes--what are advantage and how to connect a capactor in single ph,and which type of capacitor if no- what are disadvantages.
How I calculate the ELCB for circuit breakers?
How much width of the land shall have to be left below the EHT line of 440 kv as per the rule. i am told that a corridor of 35 M width is to be left free below 220 kv line. please confirm
why transformer ratinh is in KVA????/
8 Answers Apollo, Priyadarshini, Reliance,
Calculate torque developed by the 3-phase, 5 H.P., 4 pole induction motor runs at 1500 rpm A 23 N-m B 21 N-m C 10 N-m D 0 N-m
What is the purpose of SSVW, IOVW, DVDF Tests in transformer? Those who are answering, pls send mail ids also.
where used of HVDS system.
what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Breaker?
why the transformer ratings in kva
identify the components of the tube light and explain how they function???wat is inside the fluroscent tube???how it works???
How open delta used for protection?