what will hapen if secodery circuit is open of current
transformer
Answers were Sorted based on User's Feedback
Answer / thowsif_emerson_csm team
The CT Will Burn....
Why does opening a CT's secondary cause dangerously high
secondary voltage?
With the flow of both primary and secondary currents the
transformer's exciting current is very low. The secondary
current mmf serves to keep the magnetizing flux in check!
If the secondary now opens the primary current mmf produces
an exciting current 'orders of magnitude' greater than
normal. And, the resultant large increase in flux density
produces an extremely high voltage in the secondary.
Regards,
Thowsif.
| Is This Answer Correct ? | 26 Yes | 3 No |
Answer / mohankumar n , aee power plant
since I1/I2=V2/V1= K which is called as transformation
ratio if CT secondary gets openned A High voltage across
secondary will results on over heating of ct & if it is
allowed results on ct flashover. CT openned secondary
voltage depends on the line voltage & ratio. ie IF line
voltage is 415v & ct ratio is 1000/1 Amps during secondary
opennned case voltage will be 415*1000=415000 volts. this
voltage will definetly damage the ct as its insulation
level is lower than yhis.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / b.murali dhara babu
The Current transformer cores used for protection are
designed to work at low flx density during normal operating
conditions i.e at rated capacity .During the CT secondary
open conditions the flux produced in the core will become
high due to flow of current in the primary and has no
oppsing flux due to CT secondary winding . This may
causes development of the high voltage which is equal to
E=4.44 x flux x Frequency .Diring the fault conditions the
current value goes up and there by the flux value in the
core also goes up and causes very high voltage to develop
in the CT secondary . The CT secondary insulation was not
suffient to with stand the voltge stress and causes the
filure of insulation and inturn the CT .
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ritesh khimani
i think the net power that can be transfered by ct is the
diffrence between primary and secondary power.if seconbary
is made open then net power becomes primary power which may
cause the damage to the transformer.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mahesh
suppose secondary circit is open the ct is failed.we have to now ct is consist of primary and secondary windigs if secondary is opene large amount of current is flow and damage of ct.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / pushpa.m.j
Transformer is used to transmit the higher power in to
required amount that is from primary circuit to secondary
circuit .If secondary circuit opens means there is no any
current,hence transfermer is failed to transform the power.
| Is This Answer Correct ? | 2 Yes | 10 No |
Answer / santhosh
its depend on the windings if secondary more no winding
compare to primary then it do not effect it
| Is This Answer Correct ? | 2 Yes | 10 No |
why we use REF and Differential Protection in one transformers?my doubt is both protections are operated in internal fault only.why we want to use 2 protections?please clarify.
The transmission does not have options: a)Partition noise b) Flicker noise c) resistance d) Short noise and reason
how we can check new PT ? without name plate.
1 Answers Indo Power Projects,
what is the differance of acb and mcb and mccb
What is FTA card? How it works?
why transformer neutral and CT Secondary neutral is connected to earth?
what do you mean by type zero control sytem ?Give an practical example of type zero contol sytem?
What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boosting the PF Design Calculation.( Eg: for 30 KVAr required how many KW?)
17 Answers Alstom, Call Centre, EDC, HCL, Procon Engineers,
HOW DO I CALCULATE THE SETTINGS FOR THE DIFFERENTIAL PROTECTION OF A 12kV/6.6kV, 6MVA,DYN11 XMER WITH PRIMARY SIDE CTR 400/1 AND SEC SIDE CTR 600/1?
Can we step up a 230V supply to 400V using a single phase transformer??
How to calculate the Sizes of the cable required for one specific load? Is there any formula for that? ( EX: For 400KW load,50mtr Length, What is the LT cable Size required?)
How many earthing pits are requier to disapper the surge current of one lighting arrester.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)