can u tell the difference between star - star transformer
and delta to delta transformer?
Answers were Sorted based on User's Feedback
Answer / dinesh
1. Star-Star(Y-Y) Connections.I gives line voltage √3 times
phase voltage. It is economical for small high voltage
transformers as the number of turns per phase and the amount
of insulation required is less. There is no phase shift
between primary and secondary voltages. The drawback is that
the neutral is unstable because of third harmonic component
in the exciting current.
2. Delta-Delta (Δ - Δ ) Connections. The arrangement is
generally used in systems which carry large currents on low
voltages and specially when continuity of service is to be
maintained even though one of the phases develops fault.
There is no phase displacement between primary and secondary
voltages. There is no distortion of flux as the third
harmonic component of magnetizing current can flow in the
delta connected primary windings without flowing in the line
wires. The conductor is required of smaller x-section as the
phase current is 1/√3 times of the line current. No
difficulty is experienced due to unbalancing of loads on the
secondary side. The disadvantages are that more insulation
is required and the voltage appearing between windings and
core will be equal to full line voltage in case of earth
fault on one phase.
(techie.dinesh@gmail.com)
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mohd saaim
in star-star T/F primary windings are connected in star
connection and secondry winding sme as well
in delta-deltaT/F primary windings are connected in delta
connection and secondry winding sme as well
Is This Answer Correct ? | 7 Yes | 9 No |
A system having the charactristic eqation (s+1)(s+2)(s-3)=0 is (a)stable (b)unstable (c)marginally stable (d)critically stale
Size of the 60Hz and 400Hz transformers is a) same b) 60Hz Tr s larger than 400Hz Tr c) 400Hz Tr s larger than 60Hz Tr d) None of the above
how to calculate the megger values for motors and cables?
in power station what is the electrical circuit length of spacing between power transformer and lightning arrestors,for the voltage system of 230kv,110kv,33kv,22kv,11kv?
plz send me the placement interview question and answers of whizchip(technical and apttitude)..i have an interview in next.
Relative synchronous generator
is there any lightning by passer is arranged in ship like buildings?
How much kv gas generator is needed to run 2 hp and 1 hp airconditioners, plus a refrigerator and 4 Tvs
Why 11KV/440V distribution supply use for Domestic use?
3 Answers Essar, Getco, Nissan,
what is defference by mcb,mccb and mpcb
What is resistance reading of earth copper rod with grid and without grid?
for a 400kv t/m line with 10 ampere current will corona occur?