What are the steps for Testing of 6.6KV HT Panels?
Answers were Sorted based on User's Feedback
Answer / rajendran
The type of panel is not mentioned in the question, how
ever following are the general testing steps....
1) Panel allignment
2) control wiring testing
3) Power ccircuit testing
4) Instument transformer testing
5) Beaker testing if any
6) Relays testing in the panel
Is This Answer Correct ? | 62 Yes | 8 No |
Answer / rama raju (essar)
The following test are to be carried out for HT panels..
1) Functional test(In this test we can check control
wiring,power circuit wiring,Breaker Testing & loop test)
2) Relay Testing (all types of relays and power meters)
3) Meggering and hypertest.
4) polarity Test.
5) Primary Injection Testing.
6) Secondary injection Testing.
7) Breaker contactor resistance and timing.
8) MV Drop Test
9) Knee voltage Test depends upon CT.
10)Relay coil resistance & Pickup voltage and
Dropup voltage it depends upon ur relay.
11)IR value for surge Arrestor.
Is This Answer Correct ? | 50 Yes | 2 No |
Answer / siva prasad
1. Check the panel alignment
2. Check the panel wiring as per scheme diagram
3. Check the continuity of Panel wiring
4. Check the meggar values of Bus bars and HT cable
5. Check the millivolt drop test of bus bar
6. Check the status of breaker
7. Primary and Secondary injection, Polarity tests for CT
and PT of bus bar
8. Set the time for fault current objection in relay
9. Knee voltage Test depends upon CT
10. Check DC supply permanent are temporary.
11. Physical inspection for satisfaction
Is This Answer Correct ? | 18 Yes | 3 No |
Answer / c aaron franklin del
1. CT/PT Testing
2. Breaker Testing
3. Control wiring & Interpanel wiring
4. Relay Testing
5. Scheme Check
6. Bus PT and Buscoupler operation check
7. HT Busbar Megger and Hi-pot Test
8. Feeder by Feeder Commissioning
Is This Answer Correct ? | 17 Yes | 2 No |
Answer / sheikh rashid
Berque Technologies Pvt Ltd is one of the manufacturer of
earthing compound and earthing electrodes for maintenance
free, corrosion free, eliminates the step and touch
potentials. long life, good conductivity.
www.berquetechnologies.com
berquetechnologies@gmail.com
Is This Answer Correct ? | 9 Yes | 3 No |
why the the phase transformer's nuetral has been grounded
how to calculate the load on transformer..????
what will be fault level of 11 KV , 2000 A ELECTRICAL SYSTEM?
how point on wave controller works.
What is lc oscillator?
in electrical control panel. how can i choose the cable rating. (example - 11kw motor, 18-25A mpcb}
HOW TO CALCULATE CT AND VT RATIO IN PRTECTION AND METERING?
1 Answers College School Exams Tests, L&T,
It is a three inch fan and i want it to rotate to other direction .I've tried cutting the wire and reconnecting them inverse like black to white and white to black ,but it won't start rotating when i plug it in that way.And then it works again when i rejoin the wire to the way it is. I don't know what causing the problem.Is there anyone familiar with these small mortor?Any suggestion would be appreciated.Thanks!! http://i296.photobucket.com/albums/mm163/sasukebloodwheel/110527-105859.jpg
What is the difference between emf, voltage drop and potential difference?
In power generator sets, when they are coverted from 50hz to 60hz, the kva rating after conversion increases. For example, the manufacturer of a perkins 200kva @ 50Hz generator set has mentioned it to become 220kva after converstion to 60hz. What is the relation between the frequency & the KVA rating. Any formula please.
can we coorect P.F. OF 320 KVA ALTERNATOR AT LOCAL SITE WITH RATED .8 PF LAGGING.
I have raw material for making Compact-Choke for flourscent lamp of 40 Watts. We are suppose to get 0.4 amps output at end. but we are getting 0.42 or 0.44 amps and above. We have done many testings in different but nothing worked out. Please suggest me how to get the correct output. We are using 1. core winding of 700 windings of aluminium 2. E-shape iron fillings and I-shape iron fillings to surround the winding.