Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What are the steps for Testing of 6.6KV HT Panels?

Answers were Sorted based on User's Feedback



What are the steps for Testing of 6.6KV HT Panels?..

Answer / rajendran

The type of panel is not mentioned in the question, how
ever following are the general testing steps....
1) Panel allignment
2) control wiring testing
3) Power ccircuit testing
4) Instument transformer testing
5) Beaker testing if any
6) Relays testing in the panel

Is This Answer Correct ?    62 Yes 8 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / rama raju (essar)

The following test are to be carried out for HT panels..

1) Functional test(In this test we can check control
wiring,power circuit wiring,Breaker Testing & loop test)
2) Relay Testing (all types of relays and power meters)
3) Meggering and hypertest.
4) polarity Test.
5) Primary Injection Testing.
6) Secondary injection Testing.
7) Breaker contactor resistance and timing.
8) MV Drop Test
9) Knee voltage Test depends upon CT.
10)Relay coil resistance & Pickup voltage and
Dropup voltage it depends upon ur relay.
11)IR value for surge Arrestor.

Is This Answer Correct ?    51 Yes 2 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / siva prasad

1. Check the panel alignment
2. Check the panel wiring as per scheme diagram
3. Check the continuity of Panel wiring
4. Check the meggar values of Bus bars and HT cable
5. Check the millivolt drop test of bus bar
6. Check the status of breaker
7. Primary and Secondary injection, Polarity tests for CT
and PT of bus bar
8. Set the time for fault current objection in relay
9. Knee voltage Test depends upon CT
10. Check DC supply permanent are temporary.
11. Physical inspection for satisfaction

Is This Answer Correct ?    18 Yes 3 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / c aaron franklin del

1. CT/PT Testing
2. Breaker Testing
3. Control wiring & Interpanel wiring
4. Relay Testing
5. Scheme Check
6. Bus PT and Buscoupler operation check
7. HT Busbar Megger and Hi-pot Test
8. Feeder by Feeder Commissioning

Is This Answer Correct ?    17 Yes 2 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / sheikh rashid

Berque Technologies Pvt Ltd is one of the manufacturer of
earthing compound and earthing electrodes for maintenance
free, corrosion free, eliminates the step and touch
potentials. long life, good conductivity.

www.berquetechnologies.com

berquetechnologies@gmail.com

Is This Answer Correct ?    9 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

what is the diff. b/w balanced and unbalanced load..?

12 Answers  


how to reduce shorting current in a slipring induction motor

3 Answers  


How Many safety of Air circuit breaker

2 Answers  


Saving in copper achieved by converting a 2 winding transformer in to an auto transformer is determined by A voltage transformation ratio B load on secondary C quality of core material D size of transformer core

0 Answers  


Capacitor bank require for 1000amp load

2 Answers   Biodeal, Pharmaceutical,


What is core CT & it's function?

0 Answers  


I have two power supply.a)govt. power b)Captive power.3 phase load connected inside factory.when source change govt. source to captive some motor rotate reverse. Is phase sequence changes when if off & on?If I off generator & on it again is it possible to get changed phase sequence??

4 Answers   ABB,


What sort of protection scheme do you suggest for the protection of a 10 HP motor?

1 Answers   Chevron,


i completed my b.tee(eee) in 2009, but i did not join any job, i joined in my father business, now i want to join any good job, please suggest any course for me

1 Answers  


why the rating of a transformer in kva not in kw.

9 Answers  


How can we design a HVAC Plant room which includes AHU,FCU,Chillers,Cooling towers, Pumps etc & how will they work? any Drawing if possible?

0 Answers   TCS,


Does the motor power displayed on the Motor name plate is the mechnical power motor delivers or it is consumed power from the system?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)