What are the steps for Testing of 6.6KV HT Panels?
Answers were Sorted based on User's Feedback
Answer / rajendran
The type of panel is not mentioned in the question, how
ever following are the general testing steps....
1) Panel allignment
2) control wiring testing
3) Power ccircuit testing
4) Instument transformer testing
5) Beaker testing if any
6) Relays testing in the panel
| Is This Answer Correct ? | 62 Yes | 8 No |
Answer / rama raju (essar)
The following test are to be carried out for HT panels..
1) Functional test(In this test we can check control
wiring,power circuit wiring,Breaker Testing & loop test)
2) Relay Testing (all types of relays and power meters)
3) Meggering and hypertest.
4) polarity Test.
5) Primary Injection Testing.
6) Secondary injection Testing.
7) Breaker contactor resistance and timing.
8) MV Drop Test
9) Knee voltage Test depends upon CT.
10)Relay coil resistance & Pickup voltage and
Dropup voltage it depends upon ur relay.
11)IR value for surge Arrestor.
| Is This Answer Correct ? | 51 Yes | 2 No |
Answer / siva prasad
1. Check the panel alignment
2. Check the panel wiring as per scheme diagram
3. Check the continuity of Panel wiring
4. Check the meggar values of Bus bars and HT cable
5. Check the millivolt drop test of bus bar
6. Check the status of breaker
7. Primary and Secondary injection, Polarity tests for CT
and PT of bus bar
8. Set the time for fault current objection in relay
9. Knee voltage Test depends upon CT
10. Check DC supply permanent are temporary.
11. Physical inspection for satisfaction
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / c aaron franklin del
1. CT/PT Testing
2. Breaker Testing
3. Control wiring & Interpanel wiring
4. Relay Testing
5. Scheme Check
6. Bus PT and Buscoupler operation check
7. HT Busbar Megger and Hi-pot Test
8. Feeder by Feeder Commissioning
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / sheikh rashid
Berque Technologies Pvt Ltd is one of the manufacturer of
earthing compound and earthing electrodes for maintenance
free, corrosion free, eliminates the step and touch
potentials. long life, good conductivity.
www.berquetechnologies.com
berquetechnologies@gmail.com
| Is This Answer Correct ? | 9 Yes | 3 No |
What are the applications of different multistage amplifiers?Plz also write advantages of these amplifiers? Thaaaaaaaaanx
ROC converges if poles and zeros lie inside a. Origion b. Z=1
what do you mean by 1 ton in AC`s
36 Answers Bhel, Bosch, ITC Infotech,
Anybody now how to claculate the Bescom power consumption?
what is 3 phase motors
Currently what is the highest capacity (MVA) of SPPg generator available in the market?
what is the maximum temperature rating of a thhn insulated conductor?
To make a basic instrumentation amplifier, it takes A One op-amp with a certain feedback arrangement B Two op-amp and seven resistors C Three op-amps and seven capacitors D Three op-amps and seven resistors
what is the difference between concentrated winding and Distributed winding in motor?
why do we prefer -48 volt instead of -24volt or -12 volt etc. ??
to vary valtage from 0 - max a variac is necessary . so how to design for high power applications nearly about 200KW power
Why is earth connected to neutral on transfomer installations
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)