Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How can we calculate the rating of capacitor bank to be
connected for a particular load(ex.100kw)to improve the
power factor from 0.8 to 0.9?

Answers were Sorted based on User's Feedback



How can we calculate the rating of capacitor bank to be connected for a particular load(ex.100kw)t..

Answer / suneetha

The rating of capacitor bank is in kvar.Kvar rating can be
found out by power traingle.
active power=100kw
let the angles corresponding to power factors .8 and .9 be
A1 and A2 respectively
then reactive power required to improve the power factor
=100sin(A1)-100sin(A2)

Is This Answer Correct ?    18 Yes 9 No

How can we calculate the rating of capacitor bank to be connected for a particular load(ex.100kw)t..

Answer / mandeep singh

its.....kvar =capacitor bank 2 b installed,p=100kw,

kvar1=ptan(cosinverse 0.8),kvar2=ptan(cosinverse0.9)
kvar=kvar1-kvar2

Is This Answer Correct ?    7 Yes 2 No

How can we calculate the rating of capacitor bank to be connected for a particular load(ex.100kw)t..

Answer / ravikumar

kvar=kw(1.732) (TAN PHI1-TAN PHI2)
HERE PHI1=0.8
PHI2=0.9

THIS IS THE FORMULA REF; powersystems v.k. mehata

Is This Answer Correct ?    7 Yes 5 No

How can we calculate the rating of capacitor bank to be connected for a particular load(ex.100kw)t..

Answer / pasuvaraj

Mr Ravikumar, When your calculating the KVAr, you using the
KW in the Formula, How you consider the KW, The KW after
the KVAR Added or Before Added. This my doubt in your
formula you have explained

Is This Answer Correct ?    3 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

does the Trivector Meter of three phase automatically takes care of the low power factor and gives the reading accordigly or it does not take care of the Power factor while giving the readings please explain

0 Answers  


15hp motor wound by 0.9mm & 0.95mm magnet wire. at no load test it draw 4.2A current. Another motor with same condition draw 9.2A current. How can that occur? pls help

0 Answers  


What is the distance between each insulator in 33kv transformer and how can it calculate

0 Answers  


List out the the types of Mounting Light fixture?

0 Answers   HLL,


i have installed my solar site of 6.7kw and is working perfectly , can somebody tell me that how can i measure my solar irradiation kw/day/sq m ?

3 Answers  


In case of dc circuit Whether dc current will pass through capacitor after it gets charged?

2 Answers  


Define closed loop control system.

0 Answers  


Hi all I had applied for the RRB test in the ELECRICAL category. I would be pleased if any of you can sent me previous year question papers. Please forward the question papers to varshashahi@yahoo.com Thanks and regards Varsha

0 Answers  


Any one can explain if there is any harm from humming noise heard from air circuit breaker : we have 415 switch board having two incomers from transformers 3.3KV/415V , when bus coupler closed, and open one ACB incomer to work in one of the transformers, the current started hunting around 50 Amps, and heard humming noise from the air circuit breaker, although the load current was only 1200 amps while the ACB capacity is 2500 Amps, and the transformer 1600 KVA. The same didn't happen when taken the other transformer offline. Why this humming noise and current fluctuation? is there any implication or danger, bearing in mind that we just returned everything back to normal and stopped the maintenance of the transformer. Shall we go ahead and ignore this noise?

6 Answers  


We have two 1 phase heating coils having same resistance of 25ohm, but during operation one takes 3A and other 6A Is it posiible Pls. explain

5 Answers   Bhel,


1.what is the reason for transformer and lightning arrester blast in 33kv system

0 Answers   ABB,


WHY CFL can't made in shape of bulb.

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)