importance of air gap in transformer
Answers were Sorted based on User's Feedback
We know that,The air gap controls the amount of magnetic
field produced for a given current. In the equation
∫H·dL = n i , H is quite small in the iron because of its
high permeability. Nearly all of the integral accumulates in
the air gap even though the gap is very small compared to
the part of the closed path length in the iron. It reduces
the tendency of the iron to saturate to avoid harmonics in
the current.
thanking u
http://a2zengineering.blogspot.com/
z_hosen@yahoo.com
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / arockia doss.a
Actually the airgap in transformer is for transfer the
primary power to the secondary. Means the primary winding
input voltage level will be step up/down(Depends on type of
trf.) to the secondary winding.
This is exactly same with wats happening in a 3 phase ind.
motor between stator & Rotor.
Thats why we are calling ind. motor as "Rotating Trf".
Thanks ....
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / rakesh patel
It limits the short circuit current of the transformer and it also control the Saturation of the core.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / engr. kashif
None of the above answers gives a satisfactory explanation.....some1 plz elaborate it....Thanks.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nain
hi
air gap depend upon the applied voltage / range of voltage
in that gap.if it is not sufficient gap then breakdown of
the voltage will occur.
Is This Answer Correct ? | 1 Yes | 6 No |
How the over load setting for HT Motors calculated-provided in Numerical Relay
0 Answers Damodar Valley Corporation,
What is the Full form of Rccb,MCCB,
11 Answers Marriott, Maruti Suzuki, MCB, PCC, RCCB, Torrent Pharma,
what are the standard IR values should be of R-E, Y-E, B-E, R-Y, Y-B, B-R of VCB in closed condition and in open condition for 500KVA & 1000KVA transformers. and what is the acceptable range when tested by 5000V megger.
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
WHAT IS THE COOLANTS IN TRANSFORMER?
how to calculate power loss cost of aluminium conductor and copper conductor?v=500v.i=100A.x-section area=68mm.squre conductor
How to calculate the volumetric capacity of a oxygen & Nitrogen gas Cylinder if pressure is 145 kg/cm2 & water capacity of cylinder is 67 liters.
why in the three pin plug all 3 pins are cutted ?
How power cable & control cable can be differentiate from each other ?explain?
14 Answers Aster, Finolex, TCE,
why the CT ratio secondary is always divided by 5 for eg( 75/5,80/5,50/5)
On what basis primary and secondary of a transformer is chosen?
what is first ground fault & second ground fault. This is used in rotor protection of alternator.