why transformer neutrol is grounding
Answers were Sorted based on User's Feedback
Answer / mahesh sali
there having two merits of neutral grounding , no. one is
that neutral gnd. help to give additional protection
against earth fault , second one is that it will give the
balance voltage by keeping neutral at zero potential
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / mahavir jagdev
Answer No:5 is fully correct.
1. Prtects the equipment and passes the short circuit through the ground to the generating or sub-station.
2. If you do not ground the neutral, then you have a floating neutral which will cause imbalance in voltage of the other phases and the earth to neutral voltage will also come into play. Incase the other two phases have any single phase equipment hen they will get a lower voltage due to the floating neutral, which could be as high as 60-90 volts betweem earth and neutral, causing tube lights to dim etc.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / bijay
its simple like water flows from ur overhead tank when the
tank is fully filled,same is the case with trafo
during fault condition the fault current passes thru trafo
neutral to ground and thus the electrical network's
components are safe (but not 100%).
in absence of which there will be a abrupt rise in the
voltage in 2 phases (as in case of 1ph-gr. fault)
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / adeel hafeez
Transformer's neutral is grounding Because, when any Fault
is Presence in the Transformer,Or wiring going to Short C-ct,
then then Flow of current is starting and by Using ground
Wire it reaches to the Grid Station,
and when any man touches it then Nothing happening to
it.Because of Ground Wire,
in Other Words, Man's life Can be Safe by Using Ground Wire...,
If any one having Accurate Answer plz....,send it on My
E-Mail Address Adeelhafeez786@yahoo.com
Thnxxx.... for Read
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sivaraman
as said above v cant provide protection against all the
faults by groundin neutral. its onli 2 protect from phase 2
ground faults. wenever phase 2 ground faults occurs,
current wil take the return path 2 neutral 4m ground.so
the entire current wat that system delivers wil flow thro
the same phase wich was affected n to the groun(as its grnd
fault)then from ground to neutral(as its grounded). thus it
attains a closed path. the fuse of the same phase wil blow
out. thus by it protects the healthy phases n also the load
system
| Is This Answer Correct ? | 0 Yes | 0 No |
Generally H.T. side of trans.neutrol grounded through
resistor called NGR which is depends upon earth fault delay
time.At L.T. side neutrol grounded solidly .
This is because when earth fault occurs in phase, fault
current passes through neutral to earth immidiately to
avoide further damage to system.Earth fault protection
relay mounted on neutrel C.T.This relay operates properly.
| Is This Answer Correct ? | 0 Yes | 0 No |
what ispositive, negative, zero sequence impedence?
ITI r/tv trade APPLY (J.T.O VACANCEY) ALSO INCLUD AITT ELECTRONIC,WRITEEN XAM DONE 23.03.10 BUT NO RESPONCE WHY ANATHER ID gopal_gh007@rediffmail.com
What are the steps for Testing of 6.6KV HT Panels?
How do we calculate the maximum amount of current in a 300 SQ.MM cable ?
why CERAMIC material is used in insulators??
Dear friends I want to design busbar for1600 kva transformer(i.e2100 amps) what are all the factors to be considered before selectinga busbar what are all the standard sizes of busbars what is the formula for finding current of copper and aluminium busbar
Neutral CT for 45MVA 132/11 KV YNd11 Transformer. NCT REF CLASS-PS or 5P20 with 20VA burden which is suitable.
How to do cable earhing? whether by grounding Armour to ground or by running extra G.I wire along with cable? which one is preferred mostly amoung them? If the second one is more preferable how many GI wires to be run along with cable (1 or 2)?
How to determine alternating current frequency?
what is the function of turbo in dg sets
how calculate external illumintion in a compound area. for e.g. there is one open park having 600m2 area and i have to put 40w flouresent tube fitting with pole. how shall i calculate the numbers of fitting.
is it possible to minimize the copper loss?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)