Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


HT motors are generally connected in star, what will be the
effect if we connect HT motor in Delta?

Answers were Sorted based on User's Feedback



HT motors are generally connected in star, what will be the effect if we connect HT motor in Delta..

Answer / iamdon

star coonection reduces the voltage appering across each
phase by root 3 times.It means we need to design the
insulation for lower voltage which is economical.Also due
to reduced voltage reduced currrent will flow through
winding so less loss so less heating of winding so less
cooling requirement for keep the temperature rise within
limit.
All these beauty will lost in delta connection.So delta is
not preferred..

Is This Answer Correct ?    42 Yes 3 No

HT motors are generally connected in star, what will be the effect if we connect HT motor in Delta..

Answer / nishad

If we are connecting the HT motor in Star, the starting &
load current will be decrease 57% as compaire to Delta
connection.
In the cause of our HT motor (11KV - 780 FLA, 14MW)drawing
arround 4250 A at the time of starting. It's just equal to
6 times of full load current. as per manufactore, it's
locked rotor current is 4280A. so just think, what will
happened if that connected in Delta!!!!!

Is This Answer Correct ?    14 Yes 5 No

HT motors are generally connected in star, what will be the effect if we connect HT motor in Delta..

Answer / social worker

if u don't knew the answer just mind your buisness

Is This Answer Correct ?    4 Yes 2 No

HT motors are generally connected in star, what will be the effect if we connect HT motor in Delta..

Answer / sivaraman

Why not we connect HT Motor in Delta also.i am working like
this type of motors only. But starting current has 6 times
of the full load current for our motors. it may decrease
and increase as per IS ( depending on the Capacity also ).

Is This Answer Correct ?    7 Yes 6 No

HT motors are generally connected in star, what will be the effect if we connect HT motor in Delta..

Answer / girja shanker

If we connect HT motor in Delta connection then the voltage
in winding will equal to line voltage.

Is This Answer Correct ?    6 Yes 20 No

HT motors are generally connected in star, what will be the effect if we connect HT motor in Delta..

Answer / amritpal singh sidhu

I think the H.T. motor is connected in star, to take its
grounding point.

Is This Answer Correct ?    3 Yes 17 No

Post New Answer

More Electrical Engineering Interview Questions

Hi,iam a diploma in electrical engineering.rtd from indian air force in apr 2007.prsently working in reliance next link as a network maintenance engineer since 2007,can i get a job in motherson sumi.

0 Answers   Motherson, Motherson Molds and Diecasting Ltd.,


What will be the voltage impact on secondary side of two transformers with different vector groups when both voltages are compared.

0 Answers   APTransco,


What is the significance of integral controller and derivative controller in a pid controller?

0 Answers  


What is lifting power for 1 wb/m2 and 1 A magnet?

0 Answers   Techno Labs,


What is installed in PAC that is control the humidity

0 Answers   Sodexo,


what is form factor

2 Answers  


may anybody tell me the names of institute where plc programing course are conducted

1 Answers  


list the advantages of RCCB over other circuit breakers?

0 Answers  


Define phase cross over?

0 Answers  


A current of 2A flows for 10 hour through a 100 ohm resistor. The energy consumed by the resistor is:(a) 0.5 kWh(b) 4 kWh(c) 2 kWh(d) 0.02 kWh

3 Answers  


What is the estimated total hydropower potential of india?

0 Answers  


I have running 4 generator in paralel.All generators Voltages is same(470 V),KW also same (100 KW) but only No2 generator Amper is high than another generators. DG No:1,3,4 470V,100KW, 150 A DG No:2 470V,100KW,400 A

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)