HT motors are generally connected in star, what will be the
effect if we connect HT motor in Delta?
Answers were Sorted based on User's Feedback
Answer / iamdon
star coonection reduces the voltage appering across each
phase by root 3 times.It means we need to design the
insulation for lower voltage which is economical.Also due
to reduced voltage reduced currrent will flow through
winding so less loss so less heating of winding so less
cooling requirement for keep the temperature rise within
limit.
All these beauty will lost in delta connection.So delta is
not preferred..
Is This Answer Correct ? | 42 Yes | 3 No |
Answer / nishad
If we are connecting the HT motor in Star, the starting &
load current will be decrease 57% as compaire to Delta
connection.
In the cause of our HT motor (11KV - 780 FLA, 14MW)drawing
arround 4250 A at the time of starting. It's just equal to
6 times of full load current. as per manufactore, it's
locked rotor current is 4280A. so just think, what will
happened if that connected in Delta!!!!!
Is This Answer Correct ? | 14 Yes | 5 No |
Answer / social worker
if u don't knew the answer just mind your buisness
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sivaraman
Why not we connect HT Motor in Delta also.i am working like
this type of motors only. But starting current has 6 times
of the full load current for our motors. it may decrease
and increase as per IS ( depending on the Capacity also ).
Is This Answer Correct ? | 7 Yes | 6 No |
Answer / girja shanker
If we connect HT motor in Delta connection then the voltage
in winding will equal to line voltage.
Is This Answer Correct ? | 6 Yes | 20 No |
I think the H.T. motor is connected in star, to take its
grounding point.
Is This Answer Correct ? | 3 Yes | 17 No |
why we used ZNO in Lightning arrester.
What is VFD, and how its work
0.5,1,1.5,2.5,4.0.6.0,10,16 square mm electrical wires how much take maximum current in 50htz
What is the function of RCCB? What are the different sensitivity ratings & each application?
please send me last 5 year interview questions
What is the difference between KW & KVA ?
WHY HUMMING SOUND OCCURED IN HT TRANSMMISSION LINES?
What's the differs between voltage & current & emf.
how open delta PT works & what is its construction?
what are the problems faiced at dg comissiong
what is the distance between two overhead lines
WHY WE USE CABLE JUNCTION AFTER BETWEEN TANSMISSION LINE AND TRANSFORMER