Answer / iamdon
star coonection reduces the voltage appering across each
phase by root 3 times.It means we need to design the
insulation for lower voltage which is economical.Also due
to reduced voltage reduced currrent will flow through
winding so less loss so less heating of winding so less
cooling requirement for keep the temperature rise within
limit.
All these beauty will lost in delta connection.So delta is
not preferred..
| Is This Answer Correct ? | 42 Yes | 3 No |
Answer / nishad
If we are connecting the HT motor in Star, the starting &
load current will be decrease 57% as compaire to Delta
connection.
In the cause of our HT motor (11KV - 780 FLA, 14MW)drawing
arround 4250 A at the time of starting. It's just equal to
6 times of full load current. as per manufactore, it's
locked rotor current is 4280A. so just think, what will
happened if that connected in Delta!!!!!
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / social worker
if u don't knew the answer just mind your buisness
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sivaraman
Why not we connect HT Motor in Delta also.i am working like
this type of motors only. But starting current has 6 times
of the full load current for our motors. it may decrease
and increase as per IS ( depending on the Capacity also ).
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / girja shanker
If we connect HT motor in Delta connection then the voltage
in winding will equal to line voltage.
| Is This Answer Correct ? | 6 Yes | 20 No |
I think the H.T. motor is connected in star, to take its
grounding point.
| Is This Answer Correct ? | 3 Yes | 17 No |
Why are iron cores in transformers made laminated?
in 50 mw generator if field is open in full load running condition what happen and for protection which relay used?
In case of dc circuit Whether dc current will pass through capacitor after it gets charged?
what is the function of RVT
what clearance required for 4.5 mva dry type transformer?
what is differance between kvarh $ kvah
what is a composite error in current transformers, why occurs & in which it will occur i.e, either metering ct/ protection ct
what is the difference between 2 way and 4 pole selector switch???
We use ACB in LT and VCB in HT.But if we use VCB in LT and ACB in HT that what will be the effect on the system or any power range?
is it possible to flow a current between nutral and earth in a circuit? although nutral and earth having same potential diffrence? i=0/r=0A if any body now any solid reason because i am getting a triping problem in rcbo due to nutral and earth shorting???
when running 2 nos 450kva dg sets in parallel operation ,in one Dg set power factor and Kvar going to lagging and ampere suddenly going high,please give me suggestion to correct the same.
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)