how can i select the cable ratings
Answers were Sorted based on User's Feedback
Answer / a.sripathi reddy
In addition to above answer,Cable rating /size selection
based on 1.voltage drop 2.Voltage level 3.Cost
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / santosh
Cable Sizing to be selected based upon many factors, some of
these are:
1. Total connected load to be considered with 25% spare
and maximum demand current in AMPS to be calculated. This
will be maximum ampacity.
2. Derating factors such as length of cable to be laid,
Type of installation of cable in medium ( In air, Duct,
Directly buried in earth).
3. Thermal resisivity of soil at 2.5 deg C/m, correction
factor for cables, no of cables laid.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / murad
cables are used for carrying power to desired
destinations.manufacturers of cables provide apmere rating
tolerance for each cable with their booklet.for someone's
use one should follow the tables and desired amperer and
corresponding cable.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ritesh khimani
in addition to above answer i think distance upto which
cable has to csrry the power and also atmospheric condition
of the site at where the cable will be installed is also a
very important factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
What is meant by the KA-rating of a circuit breaker? In this regard, discuss the stresses experienced by the circuit breakers
what is the maximum current rating in india for home?
-What shall be short circuit current of LV switchgear for a 1000 kva, 11.415kv, 3 phase tranformer with 5% reactance.
WHY NUTRAL GROUND SYSTEM USED IN 33KV SYSTEM
what is a motor
How do you compute voltage drop and cable size over distance?
how to take the 3 phase ups input and collect single phase output
power inverter we are using 2n3773 power transister in that places we can use any IGBT ?
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
I need the recommended size for a 3 phase transformer at 13.8 KV Primary and connected loads of 3000 kVA at 4200 volts and 2375 kVA @ 480 volts AC.
what is the principle of switch gear? where its function ?
how do find power factor in practically and what it means?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)