how can i select the cable ratings
Answers were Sorted based on User's Feedback
Answer / a.sripathi reddy
In addition to above answer,Cable rating /size selection
based on 1.voltage drop 2.Voltage level 3.Cost
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / santosh
Cable Sizing to be selected based upon many factors, some of
these are:
1. Total connected load to be considered with 25% spare
and maximum demand current in AMPS to be calculated. This
will be maximum ampacity.
2. Derating factors such as length of cable to be laid,
Type of installation of cable in medium ( In air, Duct,
Directly buried in earth).
3. Thermal resisivity of soil at 2.5 deg C/m, correction
factor for cables, no of cables laid.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / murad
cables are used for carrying power to desired
destinations.manufacturers of cables provide apmere rating
tolerance for each cable with their booklet.for someone's
use one should follow the tables and desired amperer and
corresponding cable.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ritesh khimani
in addition to above answer i think distance upto which
cable has to csrry the power and also atmospheric condition
of the site at where the cable will be installed is also a
very important factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
What are the Safety Steps While Inspection the LT Panel.
different between electrical and electronics Engineering????
why C.T protection required for H.T.lines?
what is the right method of laying cable tray if we are using EOT crane in shed, better is below or up
What is the latest generation of circuit breakers called?
3 Answers Epitome, Focus Energy, Jakson, KDC, L&T,
how to find total current when kva is 30.4 given ? should we use root 3 (1.732) in the formula?
How the speed of synchronous motor changes with the variation of load?
Dear all, Can anybody tell me that how to choose CT for a specific load? I have a 200kw induction motor, which ratio CT should be installed? Is there a formula or calculation that determines the CT ratio for a load? Regards.
why neutral of 6.6 kv star connected sq. cage induction motor does not get earthed, though for earth fault protection it is must.
What the purpose of transient fault recoredr in substation
IN bateery size of positive is biger than negative .why?
Why have the transformer one earthing to their neutral? Why have the transformer many earthing to their body?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)