what is the formula for 3 phase motor starting cureent
deatials
3phase 148A delta 415v, efficiancy 94%
can we run the motor with 200A incoming supply
Answers were Sorted based on User's Feedback
Answer / birinchi narayan boruah
It depends upon designed parameter of the motor. Generally
All 3 phase Induction motors take starting current 3 to 5
times of the full load current. 200 Amps incomer can be used
for the same but its better if you go for higher rating.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prashant
P = 1.732VICosA
I = 148A
Starting current of a motor is 1.25 - 1.5% of I so you
should be able to run the motor but it will be preferable
if yu can go for the next higher rating
Is This Answer Correct ? | 5 Yes | 9 No |
I have two power supply.a)govt. power b)Captive power.3 phase load connected inside factory.when source change govt. source to captive some motor rotate reverse. Is phase sequence changes when if off & on?If I off generator & on it again is it possible to get changed phase sequence??
What is mimimum di -electric strength value for 33 KV transformer OLTC oil
why we use to always generate power below 16kv.why not at higher voltage?
how to find the 2500 KVA transformer rated primary and secondary volt and current?
How to calculate the current capacity of the 3C / 1C Al/Cu power cable???
According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.
11kv = LT 440v , how many amp.supose 440v side 5000 amp curent drown
What is the abbreviation of NGT panel
How the cable size for a motor is decided
What do you mean by linear and bilateral network?
20 Answers Automation, Disa, EGCB, Infosys, OPTCL, TICT,
what is difference between inductive and reactiveload?
Bhel supervision exam question: If 2 generators are working in a network. And if suddenly the field of anyone generator weakens. What will happen in the network? 1. The generator will run as motor 2. The generator will run as motor in reverse direction 3. The generator will take lighter load 4. The generator will take more load