how kva rating of transformer is calculated.
Answers were Sorted based on User's Feedback
My dear friends,
First of all i want to introduce myself as transformer engr
having 12 years of experience in transformer field. Now in
reply of your question, if u r asking about Name Plate of
transformer, VA = 1.732 * V * Amp
Suppose In Name Plate,
HV Volts mentioned 11000 V, HV rated current mentioned 5.25
Amp, Than Transformer capacity is
1.732 * 11000 * 5.25 = 100023 VA = 100 KVA.
In the same name plate,
LV Volts mentioned 433 V, LV rated current mentioned 133.34
Amp, So Transformer capacity is
1.732 * 433 * 133.34 = 99999 VA = 100 KVA.
If you are asking about to decide transformer capacity, u
hv to calculate your total load + future expansion load.
Than you can take decision about ur required transformer
capacity.
Is This Answer Correct ? | 48 Yes | 5 No |
the kva rating can be determined using the formula
kva=power supplied(in KW)/power factor.
so if the transformer is feeding a load of 100MW industrial
load. then the KVA rating of transformer to be used has to be
100/.85=117.647mva
we haver assumed the power factor for industrial load to be .85
Is This Answer Correct ? | 45 Yes | 9 No |
the kva of an transformer also depends on form factors.
the usage of kva 11,33,66kva all depends on form factor
as 1.11.
Is This Answer Correct ? | 12 Yes | 9 No |
First Calculate Kw Load of the plant or system which is connected to that transformer.Load is not directly calculated but calculated accordingly as per plant requirement like Continuous,Intermittent & Standby. After calculating the total load of the System in Kw.For calculate KVA of the transformer we use the Formula
KVA Load of the Tranformer - Total Plant Load Connected to transformer ( In Kw) / Power Factor
For Easy calculation ,we take PF value as 0.8.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / saravanakumar
This is the formulae for that, KVA=KW/P.F (At the time of
load calculations we should considered the power factor is
0.8 only.)
Is This Answer Correct ? | 3 Yes | 10 No |
it is very simple by knowing the formula is kva=kw/pf then
applying the formula where kw=1oo thne pf is normaly is
0.85
therefore kva=100/0.85
117.647M VA
Is This Answer Correct ? | 5 Yes | 14 No |
EXPLAIN THE FOLLWING: (1) BANDWIDTH (2) SELECTIVITY (3) RESONANT FREQUENCY (4) CURRENT MAGNIFICATION
How the unidirectional torque produced in dc motor
what is inter connected dc generator?
0 Answers Lovely Professional University,
why pure sine wave inverter used for desktop ?
i have a 4 Mva transformer 34.5 kv / 480-277 v and i used 2 parallel 3200 amp bus duct for the secondary feeder using 3 ply of bus bar ( 3/8" x 5" ) as a common where the flexible link terminated and 6300 amps breaker for the main, the lower bus duct reaches 70 degrees and the upper bus duct reaches 55 degrees when i used thermal scanner. why the temperature is not balance when the load reaches 3600 amps.
what is the difference b/w circuit breakers and relays?
when is the Ohms law is applicable?
why are we maintaining some specific gravity in battery ?
why should we connect the no load components in a equivalent circuit of transformer in parallel?why cant it be in series.
where can i get the previous years question papers for APGENCO exam.
Diode is active or passive element?
Which type of power plant is more easier to produce electrical power at economical condition?