Answer Posted / felixraj

the only diff is the knee point voltage
in metering CT this value is very low, because of this
during fault condition the ct get saturated and o/p almost zero
(metering equipments are protected from fault surge)

protection miss leads in metering CT (it may fails or
nuisance tripping)

Is This Answer Correct ?    10 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how can we say that stator magnetic field rotates with synchronous speed?can we derive?

1296


Why are short circuit ratings always 16kA,25kA,36kA and 50kA.Who has fixed these?

3809


We are preparing another project which involves Waste heat recovery from a 1 MW GE Engine. The Engine in particular gives out flue gas at 487Deg C with a flow rate of 5650 kg/hour and this can be cooled to 180 Deg C. This gives a thermal output of ~ 594 KW that is available for input to VAM via heat exchanger / boiler. Additionally 581 KW will be available from engine jacket water (temperature profile 80/ 80 Deg C and a flow rate of 50m3/hr) Our estimation is that 300 TR of cooling is possible with a suitable VAM machine(s). Please advise what is the most suitable arrangement with maximum TR and min Capital expenditure. plz reply me as early as possible

1492


As you achieve greater success with the company after some years, Will you like to be a share holder in our company?

2383


What is the Resposiblity of Electrical Utility Engineer

2411






what is the use of sdf?

1678


How to setting the volume of RTCC panel AVR (11kv) controller

1172


what is servo motor and how to work it.

1455


FEINGING DECREASES THE FLUX DENSITY IN THE AIR GAP. HOW?

1670


What is the real function of reverse power relay in generator panel while syncronising?

1599


the grid connection required for a 50 MegaWatt fotovoltaic powerplant is higher or lower than 35kv (high or medium tension)?

1430


what is a types of short circuit and what is a types of distance protection tests

1759


we have 15 ampere variyac but we want 30 ampere variyac what we do

1418


how to select battery for 15 KVA UPS with formula

2081


which type of questions asking for solar companies?

1123