How to calculate electrical Induction motor heating and
cooling time constant,11KV,2850,12P,SCIM
Answers were Sorted based on User's Feedback
Answer / kn afridi
Heating and cooling time constants are generally given by the motor manufacturer.
This is the time required by the motor to reach 63.2% of its steady state temperature T when run with full load.
Heating time constant (t) is given by the formula (1-1/e) T= (1-1/2.718) T= 0.632T
If the steady temperature T attained by the motor is 90 degree C (say) when started from cold condition, the heating time constant in minutes will be the time required by the motor to reach 57 degree C. This can be noted during the heat run test on the motor under rated condition.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / thabo
A motor with a time constant of 120 minutes is rated at 40 kW continuously .compute the half hour rating for the same temperature if it starts from room temperature every time.
| Is This Answer Correct ? | 1 Yes | 0 No |
what efficiency of transformer at 100% load
WHY THE RATINGS OF TRASNFORMER IS IN KVA?
what is the difference between equipment earth and system earth.
Enlists the applications of sampled data systems?
If we need4× 50mm sq cable but it's not available so we can pull 4×25mm sq 2cables
how to check the insulation for motor using megger?
how to find impedance , mutual indatnce in transmission lines
What is the difference between Class PX & Class X CT's
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?
Hi If connecting a temp generator 670KVA .415kv with step up Tx .415/11kv. I am given Generator impedances Z1 Z2 Z0 to 100MVA base. Do I need to work out the generator fault current by using these impedances i.e gen rating / impedance. Then use this as my source impedance for the calculations that follow.
what effect on electrical equipment if PF is gone over 0.996 in leading when provider say that its keep in minimum 0.996lagging
why we use only sine wave in ac why we do not use other wave forms
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)