What are the advantages of DOL starter?
Answers were Sorted based on User's Feedback
1.The place occupy is less.
2.can be used for high torque motors. like cruchers.blowers.
3.trouble shooting is very simple.
4.cost.
| Is This Answer Correct ? | 62 Yes | 10 No |
Answer / sathish
1. cost is less
2. compact in size
3. operation is easy
4. time of operation is less
| Is This Answer Correct ? | 21 Yes | 1 No |
Answer / jkth
main advantages of dol starter are
1.cost is less(star delta starter contains 3 contactors,a timer dol
contains a contactor only).
2.protection(it contains over current protection devices.star delta
starter also contains this)
3.less space is required
but it is used only for small motors like power less than 7.5,10Hp
| Is This Answer Correct ? | 16 Yes | 5 No |
Answer / kapil narayanrao bahadure
the advantages of DOL starter:-This is a protection device.
When motor takes large current from supply, then trip to
suplly.& safe from burn out.
When single phasing occures in the system then become
trip to sypply.by O.L.c.(over load coil).
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / v.balakrishnan
The only advantage of DOL Starter is that the cost compare
with Star Delta & Soft Starters.
| Is This Answer Correct ? | 32 Yes | 25 No |
Answer / muthupandi1418@gmail.com
1. low cost (compare star delta stater)
2.simple operation
3.troubleshooting easy
4.easy maintance
5.compact size
6.over current protection
7.line voltage direct apply to motor terminal .
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / elangkumanan
dol starter adventage that is motor protection device
another OL Relay, contactor, motor safe purpose use that is
adventage to dol starter.
| Is This Answer Correct ? | 17 Yes | 15 No |
what is daiod
what is the principle of servo motor
oil cooled transformer
why the armature coil in dc machine is round?? swagat k.
whether inrush current for lamps or capcitors should be considered cable sizing to feed that load.
Tesla is the unit of which parameter?
WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??
I want to design a heating coil of 80/20 nicrome for 3.5KW please give me the calculations choosing for physical dimensions assume coil voltage will be 110V AC assume necessary conditions
My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there any possibility of Technical Problem ?
What is meant by rotor?
For 6600/433 distribution transformer we apply secondary side 433 volts how much voltage in primary side.
what is frequency? and its importance
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)