Answer / kapil
transmitting through 66kv is better than 33kv because losses
in 66kv is less as compare to 33kv line.
| Is This Answer Correct ? | 46 Yes | 7 No |
Answer / bharat kanojia
As losses are inversly proportional to square of 'v'.
therefore 66kv could be a better option, but as the line is
a short transmission line,cost factor would come into
picture,hence accomodating everything 33kv is the most
fitting.
| Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ayush
1.as voltage of line is increased current is decreased.so
the copper losses associated wth current r reduced.but iron
losses dependent on voltage r increased.as the supply
voltage is constant so r the iron losses.but copper losses
vary wth load(load current)bcz current is less we cn say
that overall losses i.e. cu nd iron losses r reduced.
2.as nw supply votlage is increased size of current
carrying conductor reduces as current is low so less area
required for power dissipation.
3.as losses r less so higher is the effiency of line so is
the power transmission capability.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / shafiq
if there is short trasmission line it has negligible
inductive losses. there4 v prefer 33kv trasmission for this
load & order to save capital cost of the system.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ganesh9703840484
7mw load is huge load.to travel 34km it is come under
medium transmisson line.so it is necessary to reduce the
losses. if the voltage is high current becomes less.so
copper losses are reduced.so 66kv transmission is preffered.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / r k gupta
You have to find break-even cost for capital expenditure and running expenditure for both 33 and 66 kv system. Optimise the load at which 66 kv system survives the capital cost. It's simple
| Is This Answer Correct ? | 0 Yes | 0 No |
How to calculate load taken by a cable?
what may the reason for vector shift in a generator?
how i caculate the cable size for power factor correction unit for example 300kvar
why magnetising curve not start with zero voltage?
solar cell voltage?
What is RCBO? hw it works
how to do CT Burden test
What are the usege & different between UPS & batteries with charging system in in Substation?( UPS 120V AC & battery charger is 120v DC)
while running ,synchronous generator is being turned off.what will happen to the current flow??
what is self commutation how a thyristor discharges through a capacitor and inductor
how on load transformer is chnage the Tapping ?
why it is mentioned as 8/10 mva transformer why not directly 8mva or 10mva transformer. please explain me the full detailed reason.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)