Comparative difference between 33Kv & 66KV for transmitting
the load of 7 MW at a distance of 34 Km.
Answers were Sorted based on User's Feedback
Answer / kapil
transmitting through 66kv is better than 33kv because losses
in 66kv is less as compare to 33kv line.
Is This Answer Correct ? | 46 Yes | 7 No |
Answer / bharat kanojia
As losses are inversly proportional to square of 'v'.
therefore 66kv could be a better option, but as the line is
a short transmission line,cost factor would come into
picture,hence accomodating everything 33kv is the most
fitting.
Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ayush
1.as voltage of line is increased current is decreased.so
the copper losses associated wth current r reduced.but iron
losses dependent on voltage r increased.as the supply
voltage is constant so r the iron losses.but copper losses
vary wth load(load current)bcz current is less we cn say
that overall losses i.e. cu nd iron losses r reduced.
2.as nw supply votlage is increased size of current
carrying conductor reduces as current is low so less area
required for power dissipation.
3.as losses r less so higher is the effiency of line so is
the power transmission capability.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / shafiq
if there is short trasmission line it has negligible
inductive losses. there4 v prefer 33kv trasmission for this
load & order to save capital cost of the system.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ganesh9703840484
7mw load is huge load.to travel 34km it is come under
medium transmisson line.so it is necessary to reduce the
losses. if the voltage is high current becomes less.so
copper losses are reduced.so 66kv transmission is preffered.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / r k gupta
You have to find break-even cost for capital expenditure and running expenditure for both 33 and 66 kv system. Optimise the load at which 66 kv system survives the capital cost. It's simple
Is This Answer Correct ? | 0 Yes | 0 No |
what is the defination of electrical engineer.
A resistance of 50 kΩ has a conductance of:(a) 20S(b) 0.02S(c) 0.02 mS(d) 20 kS
how rated the neutral voltage of transformer and reactor, e.g. 400/220, 200MVA transformer have neutral voltage of 33kv. and reactor voltage 145kv. how this rating decided?
What are the advantages of DOL starter?
What is power factor ?What are the benefits of improved power factor & how. Please explain with examples.?
what r the main parts of central chiller plant in Air conditioner ? explain the function of each?
what is power factor ? how we can calculate the low power factor and amount of capacitor for improve that low factor ?
why anti pumping relay is not given to tripping coil of the breaker? why only to closing coil?
What is the normal earth resistance?
What is the impedence of Transformer?
what is ELCB?
What will happen when we will connect lamp in between phase and earth.