lllg,llg,ll,lg,lll which fault is severe and why?
Answers were Sorted based on User's Feedback
Answer / shonali
LLL or 3phase fault is most severe fault than the LG OR LL
or other unsymmetrical faults. 3phase or symmetrical fault
is a sudden short circuit produces currents and voltages
which are transient in nature before they settle down
| Is This Answer Correct ? | 126 Yes | 25 No |
Answer / bhuvanagiri ramesh
LG fault is most severe fault at the alternator terminals than three phase fault, because zero sequence reactance is less at the generator and fault current incase of LG fault is three times the positive sequence current. As the fault location moves away from alternator zero sequence reactance increases and three phase fault becomes more severe.
| Is This Answer Correct ? | 62 Yes | 14 No |
Answer / amritesh pandey
lll faults are most sevre but if lg fault occurs very close to
the generator terminals then it is the most dangerous fault....
| Is This Answer Correct ? | 30 Yes | 8 No |
Answer / gunasekaran
LLL fault is more danger than other fault.because large
fault current than other fault
| Is This Answer Correct ? | 35 Yes | 22 No |
Answer / akhilesh
actually l-g fault is severe at generator and l-l-l-g is severe at line.. becoz when derz l-g fault at gen .. 1.5i flows through other two phases instead of i, which is dangerous.
At lines suppose l-l-l-g occurs.. then becoz of zero voltage at tht place.. the high potential difference will make very high current to flow through lines.. which is again severe. from the formulas.. this value is more than any other current flowing through lines
| Is This Answer Correct ? | 19 Yes | 7 No |
Answer / yogesh rathod
LG fault is more severe at the generator side.
otherwise LLLG fault is more severe.
| Is This Answer Correct ? | 16 Yes | 5 No |
Answer / shashi
LLL fault is more sever than all other faults usually. But LG fault is more dangerous when generator is solidly grounded because at this condition LG fault current flows 1.5 times of three phase LLL fault current.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / harshal nemade
as symmetrical fault that is L-L-L is more dangerous. but if we calculating the fault current the LG fault current is very large as compared to other fault so from this we can conclude that LG fault is more severe than other fault.
as LG fault is take place between line and ground and ground potential is assume as zero and also having zero impedance so this fault current is very larger which is 1.5 time L-L-L fault. so according to this theory LG fault is more severe than other fault.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / aviya
In transmission line LLG fault is the most severe.
In sync m/c LG fault is the most severe.
| Is This Answer Correct ? | 0 Yes | 4 No |
If the soil resistivity is more large, how can we earthing our 11 k.v. transmission line?
What kind of preventive maintenance are there for AC induction motor?
Do these factors (settling time, peak time, steady state error, overshoot, rise time, MPOS (Maximum percent over shoot)) are the part of first order, second order, higher order, linear, non-linear, open-loop, closed-loop, homogeneous & non-homogeneous systems ?
what is negative d.c. voltage, why this voltage is used in base transciever station.
what is restircted earth fault relay,how it works? what is diffrance btwn normal earth falut relay & restricted earth fault relay?
hw the cable size can be calculated when we have watss, volts, pf, i need the forula
what is the maximum genarating voltage in india?
A system having the charactristic eqation (s+1)(s+2)(s-3)=0 is (a)stable (b)unstable (c)marginally stable (d)critically stale
Wat is da difference b/w neutral earthing and unearthed system?
what diferent amoung three phase supply?
In Power Line Communication (PLC) the wave trap is used to block communication signals from entering neighboring lines. My question is this: Why do they allow for different filtering arrangements on these wave traps? Isn't it always going to be a low pass filter since we want the power frequency to go through, and the comm signal blocked?
what is the Connected Load (kW) or Contract Demand (kVA)of mahindra nasik plant??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)