how will protect transformer agint overcurrent protection
Answers were Sorted based on User's Feedback
Answer / sunil kumar das
Full load current, we can see on name plate of the
Transformer. use the correct rating for fuse according to
full load current. If load is more than 2 mega watt then we
can use a air or vacuum type circuit breaker.
| Is This Answer Correct ? | 16 Yes | 4 No |
Answer / silpa
hi shaik, over current relay is only to sence the fault,
circuit breaker's role is to protect
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / aravind
A Differential relay can be used to detect transformer over
current.The Earth fault relay can be used to detuct over
current thro' earth.(These relays ultimately going to
initiate the circuit breaker to interupt the fault)
| Is This Answer Correct ? | 6 Yes | 6 No |
Answer / manish mishra
i agree with silpa..relay is used only for sensing but the
interruption is performed by circuit breaker...so by using
OC breaker we can protect the transformer from the OC...
| Is This Answer Correct ? | 2 Yes | 5 No |
Why air circuit breaker off due to power failure?
What is converter transformer? Diff b/w converter transformer and distribution transformer? why we use converter transformer in place of giving supply to drives?
Briefly describe three methods that are usually used by electricity suppliers to control voltage levels?
tell me working of air circuit braker.
What is the function of a pressure Switch in a Substation?
what is the difference between Resin Cast CT and Oil cooled CT?
How power factor of a transformer is calculated
Is pure capacitor load and pure inductor load is an linear load? pls justify
Why (In India) we preferably go for +-30 deg connection of transformer? what are the advantages in this connection?
dear all, How do i increase UPS (1000VA)backup time ? i have connected 2 12v wold you please 120 aH battery externally. ups charge the lead acid battery only 12.7 volt. backup time only 10.00 minuts and gose off. can any one of you help me?
What will happen if we do not provide earthing to the newtral of a power system ?
for compensate 315mh inductance ,how many capaciance required?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)