how will protect transformer agint overcurrent protection
Answers were Sorted based on User's Feedback
Answer / sunil kumar das
Full load current, we can see on name plate of the
Transformer. use the correct rating for fuse according to
full load current. If load is more than 2 mega watt then we
can use a air or vacuum type circuit breaker.
Is This Answer Correct ? | 16 Yes | 4 No |
Answer / silpa
hi shaik, over current relay is only to sence the fault,
circuit breaker's role is to protect
Is This Answer Correct ? | 7 Yes | 4 No |
Answer / aravind
A Differential relay can be used to detect transformer over
current.The Earth fault relay can be used to detuct over
current thro' earth.(These relays ultimately going to
initiate the circuit breaker to interupt the fault)
Is This Answer Correct ? | 6 Yes | 6 No |
Answer / manish mishra
i agree with silpa..relay is used only for sensing but the
interruption is performed by circuit breaker...so by using
OC breaker we can protect the transformer from the OC...
Is This Answer Correct ? | 2 Yes | 5 No |
what is the fullform of mccb
How to prepare electrical preventive maintenance plan & shedule of machine tools in manufacturing unit.
What is dynamo?How it works and what is the function of dynamo in a DG.
What accessories required to give the motor with given circuits and do you know the ratings of those accessories?
no EB power DG is not starting?
how to calculate transformer turn primary & secondary side 11kv to 420v
how to calculate the megger values for motor, cables and transformers?
why transformers are rated in KVA
What are the no-load losses for the 11000/415V transformer with the following rated capacity? 1.1500 kVA 2. 2000 kVA 3. 2500 kVA 4. 3000 kVA
Is there is any difference between AC and DC Cables
what is different the DOL Starter and Star Delta STARTER
what happen if we supply 220v dc suppy to the bulb or tube