Answer / bhanu satya prasad
if the secondary of the ct is open ,this condition will
stress ct and dangerously high voltage will be induced in
the secondary ,there may be a chance for sever hazards
Is This Answer Correct ? | 54 Yes | 2 No |
Answer / raxit
because of primary,there is flux linkage in secondary.so
current will flow through secondary.but if there is no close
path,current will not flow.but due to electromagnetic
induction high voltage will be built up across the secondary
terminal and the current transformer will BLAST
Is This Answer Correct ? | 20 Yes | 1 No |
Answer / @neesh
there should be very high voltage on secondary..it is
dangerous..............
Is This Answer Correct ? | 21 Yes | 4 No |
Never open secondary of C.T. There will be very high voltage
in the secondary winding. C.T will be blast.
Is This Answer Correct ? | 15 Yes | 1 No |
Answer / ramu
if secondary of current transformer is kept open it will
blast
Is This Answer Correct ? | 21 Yes | 14 No |
Answer / dinesh
If the secondary opened , due to inductive property a very
high transient voltage induced at the secondary side as a
result insulation of secondary side brust and it became
damaged
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / hareesh
it is normally a step up transformer,high voltage will
induse in secondery since there is no opposing flux for
primery.it is normally used for measuring purpose no current
will flows through it.flux will saturate.
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / ankush miglani 9718037333, eba
there is voltage n so current in primary side.
now due to emi voltage induced in the secondary side.
if the 2dry is open the current becomes zero, which makes
the infinite impedance n results in very high voltages
sometines in kilovolts which may produce arcing.
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / deltawye
if the secondary line of a transformer is open the current
is zero,but the voltage is still present and it depend on
the transformer rating on the secondary side..
Is This Answer Correct ? | 1 Yes | 6 No |
HOW TO CALCULATE THE LOSSES OF CURRENT FOR LT CABLE JOINTING TO MOTOR SUPPLY.
how to calculate power loss cost of aluminium conductor and copper conductor?500v,100A,68mm area squre busbar.
132 KV TRFO BUSHING BURNT WHEN A 6.6KV HAS BEEN APPLIED TO IT .WHY .ANY REASON ?
please write motor, transformer, Generator setting, fault level calculation of Tr.etc
how many types of dc batteries standards are present?
what is the principle of the single phase energy meter? and,what is the advantages and disadvantages of single phase energy meter?
How we can make sure cable size of LT cable without any parameter.
2 Answers Paradip Port, Siemens,
At what point crngo works like as crgo
Why star delta starter is preferred with induction motor?
Why there is a current in neutral line
how to calculate voltage drop in long distance cable? for an e.g lamp of 12 volt ac ,300watt is 90 meter away from supply i.e (x'mer 230 v / 12v)and i m getting 8 volts at lamp terminal ....
salam&hi, i need to know about how can i calculate an enough current for the new building before i submit it to the suppliers