what happens if generator is running leading power facotor?
Answers were Sorted based on User's Feedback
Answer / alee xain
If it is a Synchronous generator, then upon loss of
excitation it starts running at leading power factor. In
this case it would act as "Induction Generator", providing
active power to grid but taking reactive power from it.
| Is This Answer Correct ? | 23 Yes | 5 No |
Answer / sethar12
Generator will generate active power (compulsory?) and
leading reactive power. Heating effects of magnetic field
will be both on generator rotor and stator. Generator
terminal voltage increases from its rated voltage. Generator
(and grid) tripping may occur if the inductive load demand
from grid suddenly increases and generator AVR is in manual
mode (as is a normal practice).
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / deepak
in leading power factor circulating current flow in stator
& stator end ring will damage
| Is This Answer Correct ? | 2 Yes | 11 No |
Answer / suthan prabhu
If the generator is running with leading powerfactor ,Power
Utilisation is more than the power generation.
| Is This Answer Correct ? | 2 Yes | 11 No |
Answer / gi
losses decrease,the genterated power(kva) decrease.
| Is This Answer Correct ? | 5 Yes | 16 No |
Answer / pandi
if generator run at leading power factor means it supply
the reactive power
| Is This Answer Correct ? | 3 Yes | 14 No |
why rating of motor in HP ?
what is the working principle of UPS?
Why use only DC supply to charge batteries why not AC Supply??
After fault clearing in Tr line, whether the Metering core of CT is comes to normal condition from saturation region & its works as a normal condition?
Why we use 4-20 mA Analog signal for the PLC input? Why not 0-20 mA? Why not 5-25 mA?
Electrical Diagram of Electric Arc Furance from transformer to Furances
what is diffrances between fuse and breaker protection? which one is best?
1. Design a counter which counts 0, 4, 8, 2, 6, and repeats using: 1.a using JK flip flops 1.b using T flip flops 1.c using D flip flops
What is Load sharing of Transformer ?
In 3 phase induction motor 1hp current rating is 1.5 amps constant ? is correct or not ?
Generator protection &generator test
why the electrical plug point pin(earth) size in max
1 Answers Autoneum Nittoku, Bajaj,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)