What will be the average KVA rating of Auto Transformer
for 75kw 415V , 3phase induction motor




Answers were Sorted based on User's Feedback



What will be the average KVA rating of Auto Transformer for 75kw 415V , 3phase induction motor..

Answer / arulkumaran

POWER FACTOR = 0.85 (APP)
KVA = KW/PF
KVA = 75/0.85
KVA = 88.235
SO,average kva of auto transformer 90KVA (APP)

Is This Answer Correct ?    0 Yes 0 No

What will be the average KVA rating of Auto Transformer for 75kw 415V , 3phase induction motor..

Answer / baikunth

motor rating in kva = 75/0.5=150kva
so the apparent power is let 200kva.
Keeping the starting condition and fault conditions like
overload,single phasing etc. I suggest 200x3=600kva or
750kva a standard value for the motor of 75kw,supposing that
transformer ration is 1:1.

Is This Answer Correct ?    0 Yes 3 No

Post New Answer




More Electrical Engineering Interview Questions

Uses of induction motor

6 Answers   NTPC,


What is x/r ratio?

1 Answers  


what is draiv work

0 Answers  


Whai isPCC and MCC Difference?

1 Answers   Pretech Plast,


what is entropy?

3 Answers   NTPC,






if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will happen?

6 Answers   century,


we have one oven for 12 zone we are installed ir lamp in oven we control load from thyrister and 0 to 5vdc so our zone no 8 getting bright in fraction of second so what we do.. Please answer

0 Answers  


What are the conditions to be satisfied before connecting two DC generators in parallel?

9 Answers   Godrej, Bhel,


simple way to find busbar sizes??

1 Answers   SPAC,


why solinoid coil used in tripping rely?and why not other type coil?

1 Answers  


what is stalling of a motor?

2 Answers   BTCL,


WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.

0 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (4626)
  • Mechanical Engineering Interview Questions Mechanical Engineering (3697)
  • Electrical Engineering Interview Questions Electrical Engineering (15751)
  • Electronics Communications Interview Questions Electronics Communications (2634)
  • Chemical Engineering Interview Questions Chemical Engineering (761)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (79)
  • Bio Engineering Interview Questions Bio Engineering (30)
  • Metallurgy Interview Questions Metallurgy (95)
  • Industrial Engineering Interview Questions Industrial Engineering (199)
  • Instrumentation Interview Questions Instrumentation (2873)
  • Automobile Engineering Interview Questions Automobile Engineering (171)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (41)
  • Marine Engineering Interview Questions Marine Engineering (60)
  • Power Plant Engineering Interview Questions Power Plant Engineering (168)
  • Engineering AllOther Interview Questions Engineering AllOther (1331)