what is the method to measure the transformer current
carrieng capacity in three phase.
Answer / deepakindi1
same as u do in for any 3 phase circuits
ie KW=sqrt(3)*V*I*cos(@)
WKT cos(@)=KW/KVA
SO KW/cos(@)=KVA
KVA=sqrt(3)*V*I
I=KVA/sqrt(3)*V
FOR EXAMPLE CONSIDER 11KV/440V 100KVA TRANSFORMER
AT PRIMARY
I=100/sqrt(3)*11
I=100/(1.732*11)
I=5.24A
AT SECONDARY I=100/sqrt(3)*.44
I=100/(1.732*.44)
I=131.24A
Is This Answer Correct ? | 7 Yes | 4 No |
How to calulate Voltage Drop for perticular lentgh of busbar (Cu/ Al)?
What's mean HVF & HAF in Vacuum Circuit Breaker?
0 Answers Gandhi Institute of Technology and Management (GITAM), Hyundai, Jayam Engineering Works,
How to calculate the ups battery back up? give the formula.
15 Answers Cushman Wakefield, Ethio Telecom, Exide, MacLellan, Morgan Stanley, TATA,
enlist types of dc generator
Define availability (operational)?
Why human body feel electric shock?
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side
Why generally the transformer primary is connected in star & secondary in delta
Do inductive loads have distorted current waveforms ?
For load of 1 nos 3 TR Air Conditioners,6nos of 60 Watt Tibe Lights, 2 nos 200 W Outdoor Lights,1 no Coffee maker.All may work at the same timehow do I select DG Set Rating ,pLease advise the calculations
Why the Transformer Nuetral is grounded?
10 Answers Infosys, Khartoum Refinery,
63MVA,220KV/6.9KV Transformer LV side neutral is connected to Earth pit through NGR. Whether this earth pit required to connect with near by below grouding earth mat or it is to be kept separate?