what is the method to measure the transformer current
carrieng capacity in three phase.
Answer Posted / deepakindi1
same as u do in for any 3 phase circuits
ie KW=sqrt(3)*V*I*cos(@)
WKT cos(@)=KW/KVA
SO KW/cos(@)=KVA
KVA=sqrt(3)*V*I
I=KVA/sqrt(3)*V
FOR EXAMPLE CONSIDER 11KV/440V 100KVA TRANSFORMER
AT PRIMARY
I=100/sqrt(3)*11
I=100/(1.732*11)
I=5.24A
AT SECONDARY I=100/sqrt(3)*.44
I=100/(1.732*.44)
I=131.24A
Is This Answer Correct ? | 7 Yes | 4 No |
Post New Answer View All Answers
how to calculate the cable current ratingand and how much of distance the rating will be ok will the distance is incresed what the action we take
What is the difference between the relay and the circuit breaker?
How to calculate the External Resistance required for 60HP slipring motor in case no any data of the Motor is available???
Electrical Engineering
any one can explain what is the size of pvc,armoured, various sizes of powr cable dia?
How to calculate the current of Highpressure Mercury Vapour Lamp?what is the basis?whether we have to consider power factor or not?
why ss stablity limit is more transient stablity limit?
What Is Connection APFC Panel In Compony.
What is mathematical model of a control system?
Can u tell me design of switch yard
why can the rotor of 3 phase slip ring induction motor not be a 2 phase rotor?
Give two basic speed control scheme of dc shunt motor?
What are the advantages of skewing of cage rotor conductors?
What are the types of windings present in the ceiling fan? What winding will be effective first when we started the fan?What are the resistance and inductance ratios comparatively at the initial speed and full speed of the fan?
Can double compression glands be used with regular cables?