What is the function of trip neutral close switch?
Answer Posted / sanket patil
A TNC SWITCH IS ALSO CALLED BREAKER CONTROL SWITCH. IT IS
LOCKABLE IN THE NEUTRAL POSITION AND IS A THREE POLE SWITCH.
WHEN IT IS IN CLOSE POSITION THE COMMAND IS GIVEN TO THE
CLOSING COIL OF THE CKT BREAKER AND THE BREAKER CLOSES.
WHEN IT IS IN THE TRIP POS COMMAND IS GIVEN TO THE TRIP
COIL OF THE CKT BREAKER AND THE BREAKER TRIPS.
| Is This Answer Correct ? | 9 Yes | 7 No |
Post New Answer View All Answers
Control cables in S's will carry 1000v which is AC R DC? Pls answer meĀ
What is the restart inhabit setting in ABB spam150c relay (Motor protection relay)
hwat type of motor is used in thermal gas turbine hydro nuclear power plants and why
How you give clearance to a spare feeder.
can anyone explain the star-delta motor control wiring ,which wire go where and how they operate?
What is the abbreviation of NGT panel
What are the function of different components of servo motor?
Why derivative controller is not used in control systems?
If we connect a motor and generator together (I mean that the generator gives the motor electricity and the motor gives the generator movement) regardless the losses. Will the generator still generate and the motor still move?
how cables go in and come out for distribution from the feeder pillar box?
When will you multiply and devide with derating factors to the actual value while sizing the cable?
how can we select the appropriate VCB ?
What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?
dg earth connect only in the amf panel or not why
What is the Temperature to be set in Thermostat provided in Marshalling box of the Transformer / Motor.