Answer / joe 90
The rough-balance scheme shall be driven from three phase CTs fitted on the LV side of the transformer incomer circuit and on the bus section which shall be connected in parallel into rough-balance zone protection relays fitted on the bus section panel. These relays shall have a fast acting highset definite time overcurrent element and IDMT overcurrent and earth fault elements. The relays shall be set to be stable under normal and through fault conditions and to operate for an in-zone busbar fault where the fault is fed from each side (incomer and bus section) to summate at the relay. Note that for correct operation of this scheme the feeder circuits must be connected in-zone i.e. between the incomer and bus section.
A trip output from the rough-balance zone relay shall operate into the bus section trip coil and a ‘trip repeat’ output fed into the protection relays for the incomer and all feeders connected on to the faulted busbar zone via a busbar zone trip buswire. On receipt of the busbar zone trip input the incomer and feeder relays will initiate a trip output to trip their respective circuit breakers.
For a feeder fault both the feeder and bus zone protection may pickup. A means must
therefore be provided to discriminate between a feeder and busbar fault so that the bus zone protection does not have to wait to give the feeder protection time to operate in instances where the fault is on the feeder. This is done by a block signal from the feeder protection start which holds off the high set definite time bus zone protection giving the feeder protection time to operate to clear the fault. If the fault is on the busbar the feeder protection will not pick up, no block is present and the bus zone protection can operate almost instantaneously.
Where the feeder protection fails to clear a fault (e.g. circuit stuck breaker), the bus zone
protection IDMT elements will operate to trip the bus section and set the bus zone trip output high. The feeder protection start must be set low on completion of the feeder protection operation to remove any block to the bus zone protection to allow for stuck breaker situations.
| Is This Answer Correct ? | 0 Yes | 1 No |
The slip during plugging operation is given by= A 1-s B 2+s C 1+s D 2-s
if there is a voltage difference between neutral and earth when we operate any instrument for fraction of time then where is problem?
Why we use auxillary relay ? what is function of differential relay, directional o/c relay?
1 Answers Century Rayon, Mechanical,
Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example?
how can i apilly for electrical c licencese.sir,i completed B.Tech in electrical & electronics engineering in 201onot working any company
A 100KVA SINGLE PHASE TRANSFORMER 10000/200V,50HZ REQUIRES 300V AT HV SIDE TO CIRCULATE FULL LOAD CURRENT WITH LV SHORT CIRCUITED.THE INTAKE IS 1000W.THE % OF REGULATION ON FULL LOAD AT 0.8 PF LAGGING WILL BE HOW MUCH AND THE SECONDARY TERMINAL VOLTAGE ON 0.8 PF LEADING WILL BE
Why transformer neutral earthing? What is advantages?
What will be the voltage regulation of a full load and 0.80 power factor lagging load transformer when a two winding single phase transformer has a voltage regulation of 4.5% at full load and unity power factor?
what is earthing transformer? draw the winding dia.of earthing transformer.
If we give 2334 A, 540V on Primary side of 1.125 MVA step up transformer, then what will be the Secondary Current, If Secondary Voltage=11 KV?
1 Ton = ? amperes & power. How much power 1.5 TON split AC consumes in an hour at 17 C , 26 C & 28 C (thermostat' temperature).
18 Answers Aamal, Ashiana Housing, Carrier, College School Exams Tests, Eastin Hotels, Godrej, LG, Medha, Medha Servo, Onida, Orean, PEL, Sahara, Voltas,
Hi friends, i m electrical engineer i want a cdr for migration purpose so anybody have information about this then send me on jayesh_ee88@yahoo.com.please try to me
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)