What is Rough Balance Busbar Protection
Answer / joe 90
The rough-balance scheme shall be driven from three phase CTs fitted on the LV side of the transformer incomer circuit and on the bus section which shall be connected in parallel into rough-balance zone protection relays fitted on the bus section panel. These relays shall have a fast acting highset definite time overcurrent element and IDMT overcurrent and earth fault elements. The relays shall be set to be stable under normal and through fault conditions and to operate for an in-zone busbar fault where the fault is fed from each side (incomer and bus section) to summate at the relay. Note that for correct operation of this scheme the feeder circuits must be connected in-zone i.e. between the incomer and bus section.
A trip output from the rough-balance zone relay shall operate into the bus section trip coil and a ‘trip repeat’ output fed into the protection relays for the incomer and all feeders connected on to the faulted busbar zone via a busbar zone trip buswire. On receipt of the busbar zone trip input the incomer and feeder relays will initiate a trip output to trip their respective circuit breakers.
For a feeder fault both the feeder and bus zone protection may pickup. A means must
therefore be provided to discriminate between a feeder and busbar fault so that the bus zone protection does not have to wait to give the feeder protection time to operate in instances where the fault is on the feeder. This is done by a block signal from the feeder protection start which holds off the high set definite time bus zone protection giving the feeder protection time to operate to clear the fault. If the fault is on the busbar the feeder protection will not pick up, no block is present and the bus zone protection can operate almost instantaneously.
Where the feeder protection fails to clear a fault (e.g. circuit stuck breaker), the bus zone
protection IDMT elements will operate to trip the bus section and set the bus zone trip output high. The feeder protection start must be set low on completion of the feeder protection operation to remove any block to the bus zone protection to allow for stuck breaker situations.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is star delta starter? how it works? give its control and power diagram.
0 Answers Bhel, Point to Point Solution, Star Wire,
What is the List of Equipments, Instruments, Components required in Transmission of electricity from 1 substation to other substation(The equipments required in substation too)? What are the differnt IS standrds used for above equipments in Industry?
what is mean by dual digital protection in the relay field?
what is main parts of alternator.
we erected (48HP)63kva dist transformer and incoming from 11kv line,out going is 415v domastic line 2.04 km.for that actual output current is 84A. what are the losses and final output current.
what is negative and zero impedance in 3 phase induction motor ??
please give me all the Alarm .Trip ,Safety Relays & Conditions of Diesel-generators mail me on ashokbabunhce@gmail.com
what is the difference between VARIAC,AUTO TRANSFORMER,DIMMERSTAT.
what is the difference between main meter CT and check meter CT?and what is the difference between main meter PT and check meter PT?
For 415v,3phase,22kw rating of motor how to calculate MCCB rating
What is DPR relay, And what for??
Why Power generation in India is at 50Hz while in America its 60Hz so is there any advantage/Disadvantage of this ??
38 Answers Australia Visa, College School Exams Tests, Fiat, InfoPlus, L&T, NTPC, TCS,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)