Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is Rough Balance Busbar Protection



What is Rough Balance Busbar Protection..

Answer / joe 90

The rough-balance scheme shall be driven from three phase CTs fitted on the LV side of the transformer incomer circuit and on the bus section which shall be connected in parallel into rough-balance zone protection relays fitted on the bus section panel. These relays shall have a fast acting highset definite time overcurrent element and IDMT overcurrent and earth fault elements. The relays shall be set to be stable under normal and through fault conditions and to operate for an in-zone busbar fault where the fault is fed from each side (incomer and bus section) to summate at the relay. Note that for correct operation of this scheme the feeder circuits must be connected in-zone i.e. between the incomer and bus section.
A trip output from the rough-balance zone relay shall operate into the bus section trip coil and a ‘trip repeat’ output fed into the protection relays for the incomer and all feeders connected on to the faulted busbar zone via a busbar zone trip buswire. On receipt of the busbar zone trip input the incomer and feeder relays will initiate a trip output to trip their respective circuit breakers.
For a feeder fault both the feeder and bus zone protection may pickup. A means must
therefore be provided to discriminate between a feeder and busbar fault so that the bus zone protection does not have to wait to give the feeder protection time to operate in instances where the fault is on the feeder. This is done by a block signal from the feeder protection start which holds off the high set definite time bus zone protection giving the feeder protection time to operate to clear the fault. If the fault is on the busbar the feeder protection will not pick up, no block is present and the bus zone protection can operate almost instantaneously.
Where the feeder protection fails to clear a fault (e.g. circuit stuck breaker), the bus zone
protection IDMT elements will operate to trip the bus section and set the bus zone trip output high. The feeder protection start must be set low on completion of the feeder protection operation to remove any block to the bus zone protection to allow for stuck breaker situations.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

List some examples of renewable energy?

0 Answers  


What is the reasonable voltage between Neutral & Earth of an electrical system for good earthing?

6 Answers   HAL,


can any one help me out by posting something related to rvnl interview for site engineer electrical.? what is the procedure? what kinda question they ask us? how long the interview goes? and any tips? and any thing you want to share?

0 Answers  


which capacity of RCCB used for five thousand watt electricity load?

0 Answers  


what curve and rateing would you use for a three phase 0.75kw motor?

0 Answers  


how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?

0 Answers  


what is surge impedence loading

2 Answers   NHPC,


I have 200 KVA Isolation Transformer for UPS input side. & ups was having 48% load, suddenly got short what will be the reason.

1 Answers   Mukand,


why transformer rating is in KVA?

4 Answers   ABB,


Befor synchronissation of Generator what test to be carried out.pl.specify with reason.

3 Answers   Kanoria,


The 3 phase 400 hp 440 volt slip ring induction motor do not take one phase amps why ? The motor is running good condition

0 Answers  


why can't we increase the voltage by increasing the field voltage in order to get higher voltage.so that we can eliminate step up transformer

4 Answers   Bhel,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)