what is the need of reactor in between the transmission line?..like powergrid like that..
Answers were Sorted based on User's Feedback
Answer / brandon
To compensate in the case a line has too much capacitive current, or the line has usually low charge. In the latter case, if the capacitive component is too great, the line experiences overvoltages which are harmful.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ankit
To avoid Ferranti Effect in case of lightly loaded line
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sauvik biswas
With the fast expanding power system, the fault level (i.e. the power available to flow into a fault) is
also rising. The circuit breakers connected in the power system must be capable of dealing with
maximum possible short-circuit currents that can occur at their points of connection. Generally, the
reactance of the system under fault conditions is low and fault currents may rise to a dangerously high
value. If no steps are taken to limit the value of these short-circuit currents, not only will the duty
required of circuit breakers be excessively heavy, but also damage to lines and other equipment will
almost certainly occur.
In order to limit the short-circuit currents to a value which the circuit breakers can handle, additional
reactances known as reactors are connected in series with the system at suitable points. A
reactor is a coil of number of turns designed to have a large inductance as compared to its ohmic
resistance. The forces on the turns of these reactors under short-circuit conditions are considerable
and, therefore, the windings must be solidly braced. It may be added that due to very small resistance
of reactors, there is very little change in the efficiency of the system.
Advantages
(i) Reactors limit the flow of short-circuit current and thus protect the equipment from overheating
as well as from failure due to destructive mechanical forces.
(ii) Troubles are localised or isolated at the point where they originate without communicating
their disturbing effects to other parts of the power system. This increases the chances of
continuity of supply.
(iii) They permit the installation of circuit breakers of lower rating.
| Is This Answer Correct ? | 0 Yes | 0 No |
When are the directional relays used?
Why do we mix soda with water in LRS?
what the Microsoft .NET framework is?
Please clarify 1. Icw: rated short circuit working withstand capacity 2. Icu: Rated ultimate breaking capacity 3. Ics: Rated service short circut withstand capacity 4. other specification of ACB
What are the conditions to be satisfied before connecting two DC generators in parallel?
define reflection method?
how to calculate earth fault relay current and CBCT ratio
what are types of encoder
why transmission voltage is 230kv and not 220kv which is a multiple of 11
1 Answers Mettur Thermal Power Station, Siemens,
What is gross error?
How many losses in generators? how we can reduce them? and also in motors,transformers?
Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)